【Daily Topic】【HVAC Version 20170526】

2017-05-26View Original

Thread Content

Participation reward: 2 Wealth. Correct reward: 6 Wealth (please hide the answer.) Method: Advanced mode – click on the icon that combines a lock and a basket – add hidden content – submit). Multiple-choice question: The building is supplied with water using a pressure tank system; when the flow rate of the pump (or pump set) in this system is 12 m3/h, and taking into account a safety factor of 1.0 to 1.3, the number of times the pump can be started per hour should not exceed 8 times. What is then the minimum regulating volume of the pressure tank? A. 2.0m3  B. 2.5m3  C. 1.0m3  D. 2.8m3  B

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.