Questions regarding the design temperature and pressure on the high-pressure side of ammonia refrigeration systems – seeking assistance

2019-05-11View Original

Thread Content

According to the refrigeration plant design specifications, the design temperature for the high-pressure side is 150 degrees, with a design pressure of 2.0. However, for the liquid ammonia coming out of the evaporative condenser, if the design temperature is 150 degrees, then the pressure will not be 2.0. I would appreciate it if experts could advise me on how to choose the appropriate design temperature and pressure. Thank you
Reply #22019-05-13
There’s no need for a corresponding relationship between 150 and 2.0, right? The design takes into account the highest temperature and maximum pressure; these two conditions do not necessarily occur at the same time, and this value of 150 is not always required. For example, if the equipment needs to withstand a high temperature of 60°C, it is completely fine to design for 150°C as a safety margin

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.