Is a check valve needed at the fan outlet of the organic waste gas adsorption unit?

2022-11-18View Original

Thread Content

Is a check valve needed at the fan outlet of the organic waste gas adsorption unit?
Reply #22022-11-19
The pressure difference before and after the fan is low, so there is no risk of backflow; therefore, a check valve is generally not required. However, in accordance with Article 5.7.7 of the \"Fire Protection Design Standards for Fine Chemical Enterprise Engineering\" (GB51283-2020), flame arresters must be installed at the inlet and outlet of fans used to transport explosive gases.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.