With override control and the selector set to the low-value selector, why is the output of the regular regulator always lower than that of the override regulator during normal operation?
The characteristic of override control is that when the deviation between the parameter being regulated and the set value exceeds a certain threshold, another control scheme (system configuration or set value) is used for regulation; once the deviation returns to a certain level, control switches back to the normal scheme. Therefore, the use of a selector is necessary, but the selector here is not necessarily an independent device or module; it can also be an internal function of a device or module, such as a dedicated single-loop override regulator. I don’t see your system diagram, but based on what you’ve said, it’s likely that when the liquid level fluctuates within a certain range, only the main disturbance affecting the liquid level – namely the steam flow – is adjusted. Structurally, this constitutes a single-loop control system for steam; from a control perspective, it represents a feedforward control mechanism for the liquid level ; When the liquid level fluctuations exceed a certain range, the liquid level signal (via a regulator) is used as the setpoint for steam regulation; structurally, this constitutes uniform control of both the liquid level and the steam, while from a control perspective it represents a feedforward control system with feedback based on the primary parameter (the liquid level). If this switching is carried out automatically by a selector, such a system can be referred to as override control; the override mechanism determines the problem on its own, generally without the need for human intervention.