The pressure pump on the second floor of a residential building is connected directly to the outdoor piping network, which can provide a pressure of 0.28 Mpa. The static water pressure required to deliver water to the most unfavorable point in the distribution system is 0.54 Mpa; the total head loss in the piping system is 0.08 Mpa (including a head loss of 0.01 Mpa due to the water meter). The outlet head required at the most unfavorable point in the distribution system is 0.05 Mpa. The head of the water pump is calculated to be ( ) Mpa. Answer: 0.39
Reply #22019-10-06
(0.54+0.05+0.08)-0.28=0.39Mpa
Reply #32019-10-07
(0.54+0.05+0.08)-0.28=0.39Mpa

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.