2018-05-23View Original

Thread Content

Components of the mixed refrigerant: propane, ethylene, methane, nitrogen; ethylene accounts for nearly 50% of it. The amount of refrigerant consumed during operation is relatively high, and the cooling capacity runs out after a while. Please analyze the reasons! Thank you! ! !
Reply #22018-05-23
The mixed refrigerant is self-circulating; it either leaks or accumulates in some process
Reply #32018-05-23
How to deal with leaks? Most pipelines have insulation layers; can’t they all be removed?
Reply #42018-05-24
We encountered this problem as well; we checked the safety valves on the refrigerant pipes, the flange valves of the compressor, and the drain valves, and eventually found that a valve in one of the safety valve circuits was leaking. After shutting down the system for inspection, we discovered a leak in the compressor cooler. This is provided for reference only
Reply #52018-05-24
I don’t know what good methods there are···
Reply #62018-05-25
This might leak, but there may also be accumulation in the cold box during operation.
Reply #72018-05-27
Check the heat exchanger; it’s very likely that there is a leak inside it.
Reply #82018-05-28
Check if there is a problem with the phase distribution – could there be too much of the heavier component and too little of the lighter one? After recombination analysis is performed during operation, the cooling capacity will decrease.
Reply #92018-05-29
If the group distribution ratio is fine, then it might be due to accumulation in the pipes. If it’s a leak, it should be easy to detect
Reply #102020-12-20
It depends on your system; a large circulatory system does exist
Reply #112020-12-21
This is too general; there are many factors involved, such as the reasons for leakage, the pressure of natural gas, temperature, and the pressure of the refrigerant entering the cold box, etc

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.