There are no manholes on the storage tank, so radiographic testing cannot be carried out. Is it possible to use ultrasonic testing instead?

2019-05-28View Original

Thread Content

There are no manholes on the storage tank, so radiographic testing cannot be carried out. Is it possible to use ultrasonic testing instead?
Reply #22019-05-28
Yes, but it requires the approval of the original design team.
Reply #32019-05-28
According to the specifications, if RT is indicated on the drawing, approval from the designer is required. In current standards, UT holds a status roughly equivalent to that of RT; however, UT has a lower ability to detect surface and near-surface defects, so it needs to be supplemented by MT or PT
Reply #42019-05-29
1. If the design has been specified as RT, design modification procedures must be followed, and written consent from the original design unit is required before implementation. 2. For ultrasonic testing, there is a requirement regarding minimum thickness. 3. It must be recordable ultrasound or TOFD.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.