Regarding the selection of styrene breather valves

2021-03-25View Original

Thread Content

If the design of the styrene storage tank follows GB50341 (which specifies that the negative pressure should be greater than -250 Pa), the vacuum pressure is set at 0.25 kPa. Table 1 of SY-T 0511.1-2010 \"Attachments for Oil Storage Tanks – Part 1: Breather Valves\" specifies that the suction opening pressure is -295 Pa, which is lower than 0.25 kPa! So how should one choose the breather valve for this tank?
Reply #22021-03-25
It’s not necessary to follow the standards; we can operate at the pressure required by the customer
Reply #32021-03-31
GB50341 does not specify the negative pressure for breather valves. The pressure of the breathing valve is the basis for the design parameters of the storage tank. If the storage tank is existing, the positive and negative pressures at which the breather valve operates must not exceed the design pressure of the tank.
Reply #42021-03-31
It seems that it is specified that a normal-pressure tank must not have a pressure lower than -250 Pa; a pressure below this value does not qualify as that of a normal-pressure tank. Styrene storage should be at atmospheric pressure, which is where the conflict lies
Reply #52021-03-31
Regarding the negative pressure of 0.25 kPa, it mainly relates to the question of which section should be used in the calculations for tanks; do not let the term \"atmospheric pressure tank\" confuse you. The design negative pressure for many storage tanks is greater than -0.25 kPa; the vent valve can be selected accordingly.
Reply #62021-03-31
However, when selecting a breather valve, it is necessary to calculate whether it meets the ventilation requirements, and design negative pressure is involved in this process. If the designed negative pressure is higher than 295 Pa, the calculations will be incorrect (see the calculation example in Section 4.3 of Appendix A of SYT 0511.1-2010 for details)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.