There are Class A storage tanks as well as ordinary storage tanks inside the fire dike. Are there any spacing requirements between Class A tanks and ordinary tanks?

2023-03-29View Original

Thread Content

There are Class A storage tanks as well as ordinary storage tanks inside the fire dike. Class A storage tanks have specific spacing requirements; are there also spacing requirements for Class A and ordinary storage tanks?
Reply #22023-03-29
Yes, there are also spacing requirements between Class A tanks and ordinary storage tanks. According to the \"Code for Design of Tank Farm\" (GB50183), fire dikes should be installed around the outermost perimeter of the storage tanks, and there should be a distance of at least 10 meters between storage tanks holding Class A liquids and other tanks. If both types of storage tanks are located within a fire dike, the distance between them should meet the spacing requirements for Class A liquid storage tanks at the very least. This ensures safe production and prevents chain reactions in the event of a fire. .

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.