Recently, for a project, the client requested that the 35KV substation and the DCS cabinets be located in the same building. The left area of the building serves as a substation, housing transformers and high/low voltage distribution cabinets. Auxiliary rooms such as air conditioning units and offices are located in the middle part of the building, while the DCS cabinet room is situated in the right area of the building. The distance between the DCS cabinet room and the power distribution room is approximately 30 meters. Is there anyone with more experience who can take a look and see if this meets the regulatory requirements? Can high-voltage substations cause electromagnetic interference in the cabinet room? Will the fault voltage resulting from the grounding failure in the high-voltage system be transmitted to the control system’s grounding system via the equipotential bonding of the building, and could this have an impact on the control system? Thank you so much!
Reply #22019-09-06
It is not recommended to locate it together with the substation; if, due to objective constraints, the two structures must be placed side by side, an electromagnetic isolation layer must be installed between them!
Reply #32019-09-07
The regulations clearly state that one must stay away from substations, as they cause interference.
Reply #42019-09-07
DCS systems are sensitive to interference and should be installed separately. Under normal circumstances, proper shielding prevents any problems; however, if grounding and shielding are not done properly, unexpected malfunctions that lead to tripping can occur, and it will be difficult to explain such situations.
Reply #52019-09-09
Which standard is it? Thank you so much!
Reply #62019-09-09
HG/T 20508-2014 Code for Design of Control Rooms
Reply #72019-09-10
GB 50174-2017 Code for Design of Data Centers (the old version was titled Code for Design of Computer Rooms in Electronic Information Systems) 4.1.1 The location selection for a data center shall meet the following requirements: …… 7 It should be avoided from being affected by strong electromagnetic field interference; …… 6 Architecture and Structure 6.1 General Provisions 6.1.5 The main machine room and auxiliary areas should not be located directly below areas where water is used, nor should they be situated adjacent to sources of vibration and electromagnetic interference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.