May I ask how the start and stop of motors controlled by DCS are achieved in the electrical cabinet room? Thank you

2018-10-27View Original

Thread Content

For example, to start the device, the control signal is connected to the coil of the AC contactor; to stop it, a normally closed switch is connected in series with the coil. So how are functions such as fault detection, emergency stop, and operation indication achieved? Thank you
Reply #22018-10-27
Thank you\ud83d\ude0a
Reply #32018-11-02
The device that physically controls the start and stop of a motor is a contactor, or an electrically operable circuit breaker. The DCS provides one or two passive node access circuit breakers or contactors to enable remote control of the motor. The control logic is implemented in the DCS software. The control nodes are wired directly into the switchgear.
Reply #42018-11-05
The principle of DCS in controlling motors can be understood through the following points. First, examine the control schematic diagram (it is important that process engineers specify the control requirements). Second, motor start/stop control can be carried out through on-site control (i.e., control at the production site), remote control (i.e., DCS control), or MCC control (control via the electrical panel; this may not be necessary in some processes). The on-site start/stop buttons, the panel-mounted start/stop buttons, and the output signals from the DCS (which are usually sent to the relay circuits within the electrical panel) are connected in series to form a hardware circuit that controls the start/stop of the motor. Third, motor interlock controls (such as shutdown in case of faults, emergency shutdowns, or process-related interlocks) are typically implemented through programming in the DCS, with the resulting signals being sent to the relays in the electrical panel; these signals are then connected in series or parallel within the control circuit to achieve the interlock functionality. Of course, emergency shutdowns and fault-induced shutdowns usually involve both hard control (through electrical components) and soft control (through logical programs). Fourth, read the drawings more often on your own
Reply #52018-11-05
It is generally achieved through communication with intelligent motor protectors

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.