How should emergency lighting be installed in a small gas station without a control room?

2019-12-03View Original

Thread Content

As the title suggests, for a small gas station, how should emergency lighting be arranged? There is no fire control room, and it’s not a residential building; the height is definitely below eight meters! Then is it necessary to use Type A lighting fixtures? If it’s not used, are there any standard references? Thank you
Reply #22019-12-03
Type A evacuation lighting is installed in the business areas and canopies. The electrical section of the \"Design Code for Gas Stations\" specifies requirements regarding the location of emergency lighting, with Type A lighting to be installed in areas up to 8 meters in height
Reply #32019-12-05
I get it; in other words, since there is no control cabinet of this type, only a centralized power-based, non-centralized control system can be used! It’s so uncomfortable
Reply #42019-12-05
Mm-hmm, thanks! I see. In other words, since there is no control cabinet of this type, only a centralized power supply-based, non-centralized control system can be used. . . . . It’s so uncomfortable
Reply #52019-12-06
Yes, a few emergency lights won’t be enough; a dedicated power distribution box is also needed
Reply #62019-12-06
Yeah, right. Does the expert have any schematic diagrams for emergency lighting distribution systems of the centralized power supply with decentralized control type? Just send a picture! I’ve never done this! ------Some naive person who’s too shameless to ask for things: lol
Reply #72019-12-07
I can’t send pictures. L means you draw a square and write on it \"Emergency lighting distribution box, with centralized power supply.\" In front of the square is the incoming wire, and the outgoing wire is shown behind it. Specifically, you can find a manufacturer online and draw a simple diagram based on their instructions.
Reply #82019-12-10
Well, I get it now! Haha, thanks!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.