Interlock shutdown condition for the hydrogenation reciprocating fresh hydrogen compressor: lubricating oil pressure below 0.15 MPa. Oil injector failure led to shutdown (not in use); the stator temperature of the main motor was greater than 135 degrees. The main motor start switch is closed. Are everyone’s press shutdown conditions the same?b. Motor winding temperature is extremely high: 135°C
c. Leakage in the cooling water for the LIAHH811 motor
e. Position of the ZSHH806 turntable device
f. Locking of the ZSHH807 turntable device
g. Low purge pressure of the motor
h. Start/stop buttons on DCS, LOLP, UCP, or LCP
i. High vibration levels
j. Low pressure at the primary inlet (one of two options): 2.38 MPaG
k. Low pressure at the secondary inlet (one of two options): 4.36 MPaG
l. Low pressure at the tertiary inlet (one of two options): 8.44 MPaG
m. Low oil pressure in the frame (one of two options): 0.15 MPaG
n. Pressure at injectors PT847A1 and PT847A2 is low simultaneously, and this condition persists for more than 10 minutes: 0.14 MPaG
o. Extremely high exit temperature of cylinder 3# at the primary stage (one of two options): 138.9°C
p. Extremely high exit temperature of cylinder 5# at the primary stage (one of two options): 138.9°C
q. Extremely high exit temperature of cylinder 6# at the secondary stage (one of two options): 138.6°C
r. Extremely high exit temperature of cylinder 4# at the secondary stage (one of two options): 138.6°C
s. Extremely high exit temperature of cylinder 1# at the tertiary stage (one of two options): 127.3°C
t. Extremely high exit temperature of cylinder 2# at the tertiary stage (one of two options): 127.3°C
u. Motor failure within 5 minutes due to XA842 (from MCC)
v. Failure in loading the motor due to XA843
w. The exciter at XS832 is not synchronized
x. High liquid level in the inlet buffer tank for PLANT ESD at XS817; the outlet electric valve is closed