Design fire protection codes require that for fully pressurized and semi-refrigerated liquid ammonia storage tanks, fixed water spray systems and mobile fire cooling water systems should be employed. Should the liquid ammonia tank of a reformation unit be equipped with spray protection? What are full-pressure and semi-frozen types? The fire cooling water system for fully frozen liquid ammonia storage tanks is designed in accordance with the requirements for steel single-layer protection tanks used on the outer walls of fully frozen liquefied hydrocarbon storage tanks. What is the concept of fully frozen?
What size counts as a storage tank? Our horizontal tank has a volume of 3.7 cubic meters; it actually serves as a buffer tank at the inlet of the ammonia compressor
Full-pressure type: The temperature inside the storage tank is usually at room temperature, and pressure is used to prevent liquid ammonia from vaporizing. Fully refrigerated type: A refrigerator is used to keep the temperature inside the storage tank below the boiling point of liquid ammonia, preventing it from vaporizing; operates at atmospheric pressure. Semi-frozen: somewhere in between the two. There is certain pressure, and the temperature must be low. 3.7 m3 is too small; there’s no need for fixed sprinklers – just ensure good insulation to prevent exposure to sunlight.
It’s time to spray now. For such small storage tanks, it is sufficient to refer to the guidelines for specialized ammonia-related treatment.