Do overhead liquefied petroleum gas pipelines need insulation? Are there any regulatory requirements? The medium temperature is 15 to 60°
Reply #22012-05-29
It’s not necessary. Just avoid bag-shaped bends where water can accumulate, so there’s no risk of freezing in winter.
Reply #32012-05-31
The overhead liquefied petroleum gas pipeline is grounded every 80 meters to eliminate static electricity generated by the flow of gas inside the pipe and friction against the pipe walls. The grounding must be reliable; its resistance should not exceed 10Ω. Additionally, conductive bridging wires should be welded at all flange and threaded connections.
Reply #42012-06-04
Are there any specifications? Grounding of liquefied petroleum gas overhead pipelines
Reply #52012-06-06
For LPG pipelines, we generally provide insulation to prevent heat loss, or protection from sunlight.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.