Cable length issue

2012-06-05View Original

Thread Content

The distance from the fire alarm panel in that area to the plant-wide fire alarm panel is 960 meters; therefore, 10*2.5 control cables are required. Question 1: The signal transmitted is a digital one. Over a distance of 1000 meters, can the signal be transmitted using the aforementioned control cable? Question 2: This cable is used for fire alarm systems – is it sufficient to use ordinary fire-resistant cables, or are there other requirements specified in the standards?
Reply #22012-06-05
Install strictly in accordance with the requirements of the product manual; try not to use it to its limit – generally, use 80% of the recommended capacity!
Reply #32012-06-09
Fire protection system wiring mostly uses a bus topology; for transmitting digital signals, low-capacitance twisted-shielded cables should be used, rather than control cables! Furthermore, cables for fire alarms must possess flame-retardant and fire-resistant properties! Welcome to communicate!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.