Compressor installation technical plan
Thread Content
Installation Plan for Compressors in the Synthesis Unit of Jiangsu Linggu Chemical’s 300,000 tons/year Ammonia Synthesis ProjectPrepared by: Reviewed by: Approved by: Signed by:
Quality: Safety: Jiangsu Linggu Large-scale Fertilizer Project Department, Sinochem No. 13 Company
August 10, 2008
Compressor Installation Plan
1. Overview
1.1 Project overview and characteristics: The synthesis unit of Jiangsu Linggu Chemical’s 300,000 tons/year ammonia synthesis project features three centrifugal compressors in the compression section – the syngas compressor, the new ammonia compressor, and the refrigeration compressor. All of these are of centrifugal design and driven by steam turbines; each of these units has a large capacity. Among them, the syngas compressors and refrigeration compressors are both second-hand (used imported equipment from abroad) ; The ammonia compressors are supplied by SHENGU, while the extraction-condensing steam turbines are supplied by HANGQI ; It features advanced technology and requires high precision in installation; (imported equipment from abroad lacks technical documentation, which poses significant difficulties for construction), there are high requirements regarding construction safety, and the construction process is challenging. 1.2. List of Unit Equipment Parameters 1.2.1 List of Main Design Parameters for Ammonia Compressors Table of Ammonia Compressor Parameters Name, Type, Flow Rate, Inlet Pressure (MPa), Outlet Pressure (MPa) Steam Turbine, Extraction Condensing Type: 0–72,000 Kg/h, 10.01, 0.014, 10,600, 8,073 Ammonia Compressor, MCL707+3MCL706, Centrifugal Type: 34,634 Nm3/h, -0.04, 1.66, 65,814, 7,936 1.2.2 List of Main Design Parameters for Synthesis Gas Compressors Table of Synthesis Gas Compressor Parameters Name, Type, Flow Rate, Inlet Pressure (MPa), Outlet Pressure (MPa), Weight (Kg), Rotational Speed (r/min) Backpressure Turbine, GJMV-DC: 289,397 Kg/h, 10.01, 3.8, 6,804, 13,000 Condensing Turbine, GJMV: 30,426 Kg/h, 3.82, 0.013, 11,340, 13,000 Compressor Stage 1, 2BC9: 6,827 m3/h, 7.24, 7.24, 20,684, 5,600 Compressor Stage 2, 2BF9: 2,620 m3/h, 17.24, 17.24, 18,552, 5,270 1.2.3 List of Main Design Parameters for Refrigeration Compressors Table of Refrigeration Compressor Parameters Name, Type, Flow Rate, Inlet Pressure (MPa), Outlet Pressure (MPa), Weight (Kg), Rotational Speed (r/min) Refrigeration Compressor Turbine, Medium-Pressure Condensing Type: 47,042 Kg/h, 3.82, 0.015, 12,383, 7,035 Compressor Stage 1, 4C57: 35,254 m3/h, 0.55, 0.55, 17,600, 6,700 Compressor Stage 2, 7CK45: 25,935 m3/h, 1.03, 2.07, 15,105, 8,900 2. Basis for Preparation 2.1 General Specifications for Construction and Acceptance of Mechanical Equipment Installation Projects, GB50231-98 2.2 Specifications for Construction and Acceptance of Chemical Machinery Installation Projects (General Provisions), HG20203-2000 2.3 Specifications for Construction and Acceptance of Chemical Machinery Installation Projects (Centrifugal Compressors), HGJ205-1992 2.4 Specifications for Construction and Acceptance of Compressor, Fan, and Pump Installation Projects, GB50275-98 2.5 Safety Technical Specifications for Petrochemical Construction, SH3505-1999 2.6 Specifications for Lifting Operations in Engineering Construction, HG20201-2000 3. Conditions and Preparatory Work Required Before Unit Construction 3.1 Conditions Required Before Unit Construction 3.1.2 All civil engineering work related to the unit must be completed and approved upon inspection ; 3.1.3 The installation environment should be clean. The ambient temperature should not be below 5° ; 3.1.4 Set up facilities such as workrooms, warehouses, and shelves within the framework, with reliable dust and rust prevention measures in place, along with dedicated personnel on duty ; 3.1.5 Install reliable fire extinguishing equipment in the warehouse and around the shelves ; 3.1.7 Water, electricity, gas, and lighting for construction must be connected and ready for use ; 3.1.8 The lifting equipment used for installing the units inside the plant must pass trial operation tests ; 3.1.9 The following technical documents shall be available prior to the installation of the unit: 3.1.9.1 Certificate of conformity issued by the manufacturer of the unit (including certificates confirming the quality of the important components and parts) ; Quality certificates for random pipes, fittings, valves, etc ; Hydraulic test record for casing and auxiliary equipment ; Rotor Manufacturing Quality Inspection Certificate ; Rotor dynamic balance and impeller overspeed test records ; Machine assembly record ; Machine trial operation record). 3.1.9.2 Elevation and plan layout diagrams of the unit, foundation diagrams, assembly diagrams, system diagrams, and piping diagrams, as well as installation, operation, and maintenance manuals. 3.2 Preparatory work before unit installation 3.2.1 The installation plan has been approved and communicated to the team. 3.2.2 Before installation, a technician assigned to the project shall organize all construction workers to undergo technical training. Detailed study and guidance will be provided regarding the project’s quality standards, occupational safety and health, environmental protection, as well as project schedule objectives. This includes information on the unit’s processing procedures, machine structure, design drawings, manuals, regulations, standards, and requirements for installation, all in conjunction with the manufacturer’s instructions. To enable all construction personnel to gain a deeper understanding of the unit’s structure and installation requirements, as well as to master the construction methods and procedures proficiently, thus ensuring adequate preparation for maintaining the quality and schedule of the unit’s construction. 3.2.3 All kinds of record forms, instruction diagrams, tools, and measuring instruments required for unit installation are available in full. 3.2.5 Equipment installed at the bottom of the machine and connected to it should be lifted into place in advance and initially aligned; blind plates should be installed on the flange connections to the machine ; 3.2.6 Remove dirt such as paint, casting sand, and rust from the areas where the unit base comes into contact with concrete. 4. Construction procedures, methods, and technical requirements 4.1 Construction procedures for compressor units Note: As comprehensive documentation for ammonia compressor units is currently unavailable, this plan describes the installation process in accordance with standard specifications only. 4.3 Unpacking inspection and storage of unit equipment 4.3.1 Unpacking inspection of equipment The unpacking inspection of equipment must be carried out jointly by an inspection team composed of the construction party, the supervisor, and representatives from the manufacturer. When opening a device, appropriate opening tools should be selected to avoid damaging the equipment inside the box. c Verify according to the packing list whether the names, models, specifications, quantities of the equipment components, as well as the accessories, spare parts, auxiliary materials and tools, are complete, along with the equipment’s factory certification and other technical documents. Check the external quality of the equipment; any damage, rust, or defects on the surface of the welds should be recorded and photographed ; The controversial aspects among them shall be resolved through joint consultation. Check that the random drawings, instructions, product certificates, and technical documents such as quality certificates for the main materials are complete and meet the requirements of the contract. h Fragile instruments and small parts should be stored properly. The technical documents related to unboxing should be kept by a designated person. The i-device should be delivered in one go whenever possible to avoid additional handling. After successful acceptance, the personnel involved in the inspection should jointly sign the acceptance record and carry out the handover procedures. 4.3.2 Storage of equipment a Storage method: Large equipment and materials are stored on outdoor wooden racks, covered with tarpaulins. Conduct a pressure check on equipment with internal nitrogen filling; if a drop in pressure is detected, replenish nitrogen ; For precision equipment and spare parts, a dedicated storage area must be established; these parts should be placed on shelves after appropriate protective measures have been taken, and labeled. It is strictly prohibited to stack them directly on the floor. Stainless steel equipment and materials should be stored separately, either outdoors or on indoor wooden platforms, depending on their material composition and structure, to ensure proper protection. b Management method: Each piece of equipment and material on site is assigned a unique number, and a detailed layout diagram showing their storage locations is drawn, with the corresponding numbers indicated on the diagram. A ledger is kept for all equipment and materials that come in or go out, and this ledger is managed in conjunction with the delivery orders related to such transactions. All equipment ledgers, delivery orders, and the layout diagrams of where the equipment and materials are stored are managed using a computer system. 4.3.3 General requirements for equipment loading and unloading Equipment should be handled with care to ensure stability, and necessary protective measures must be taken when lifting precision equipment. 4.4 Acceptance and Handling of Unit Foundations 4.4.1 Foundation Acceptance 4.4.1.1 Organize a foundation acceptance team composed of the civil engineering contractor, the installation contractor, the design unit, the supervision unit, and the owner to conduct the acceptance of the foundation and issue an intermediate handover certificate. 4.4.1.2 The outer surface of the foundation shall be smooth, free from defects such as cracks, honeycombing, voids, or exposed rebar; it shall be accompanied by a quality certificate and measurement records. 4.4.1.3 The equipment foundations and embedded parts shall be inspected in accordance with the civil construction drawings and equipment installation drawings. The longitudinal and transverse centerlines of the foundation, its elevation, as well as the positions of the anchor bolt holes shall be rechecked. The foundations of ordinary equipment shall meet the following requirements:
Name of deviation | Allowable deviation (mm)
Foundation coordinate position (longitudinal and transverse axes) | ±20
Distance between different surfaces of the foundation | +0/-20
Dimensions of the upper surface of the foundation | ±20
Flatness of the upper surface of the foundation | [5 ‰ over the entire length]
Verticality | 5 ‰ over the entire height
Position of the center of the reserved anchor bolt holes | ±10
Depth | 0~+20
Perpendicularity of the hole walls | 10
Elevation of the embedded anchor bolts (top end) | 0~+20
Center distance (on both sides at the root and top) | ±20
Elevation of the embedded movable anchor bolt anchor plates | ±20
Center position | ±5
Levelness | 2
4.4.1.4 For the foundations of the three compressors, in addition to meeting the above requirements, they shall also comply with the following requirements: In accordance with Article 2.3.1 of the Code for Construction and Acceptance of Machinery and Equipment Installation GB50231--98, inspections shall be carried out on the foundation position, geometric dimensions, and quality of the machines. The longitudinal and transverse centerlines, axes, and elevation of the foundation shall be clearly marked ; c. According to the technical documents such as the machine foundation drawings and assembly drawings provided randomly, check that the external dimensions of the foundation, the center lines in the longitudinal and transverse directions, the distance between the center lines of the foot bolt holes and the axis, the distance between the centers of the foot bolt holes, the depth of the embedded foot bolt holes, and the specifications of the sleeves for anchor plate-type foot bolts all conform to the drawings ; For the reserved holes, the anchor bolts should be inserted vertically into the holes, and the distance corresponding to value a should not be less than 15 mm, as shown in Figure 1. The dirt, debris, and standing water on the base surface and in the anchor bolt holes must be removed completely. After the foundation inspection and acceptance are successful, the installation unit and the civil engineering unit shall go through the handover procedures, with the relevant departments signing on the acceptance certificate to give their approval. 4.4.2. Basic surface treatment procedures and methods 4.4.2.1 Basic surface treatment procedure 4.4.2.2 Creating a rough surface on the surface of the base secondary grouting layer ; The pitting depth should be greater than 10 mm, with a density of 3 to 5 pits per square decimeter; moreover, the foundation surface must not have any loose layers or oil stains ; (During work, care should be taken to protect the baseline of the unit foundation to facilitate redrawing it.) ; 4.4.2.3 Excavate a grouting pit at the position corresponding to the machine’s jacks or adjustment shims on the foundation; remove any debris from within the pit. After soaking it in water for about 30 minutes, drain the water from the pit. Fill the pit with grout of a higher grade than that used for the foundation grout, place the support pads in place, and level them using a level. The allowable tolerance is 2 mm/m; the allowable tolerance for the elevation of the top surface of the support pads is ±5 mm, as shown in Figure 2. 4.4.2.4 Recalibration of the installation reference line on the foundation: Before installing the embedded support pads, debris and oil stains on the foundation surface should be removed. The longitudinal and transverse center lines as well as the center lines of the foot bolts should be marked with ink lines, and the elevation levels should be indicated on the sides of the foundation using red triangles. 4.4.2.5 The support shims of the steam turbine are arranged according to the structure of the machine base and the number of anchor bolt holes ; Moreover, no more than four shims are allowed per group; the thicker ones are placed at the bottom, the thinner ones on top, and the thinnest one in the middle. The total height shall not exceed that of the secondary grouting layer. One pair of inclined shims is permitted per group, and the offset area between the two inclined shims shall not exceed 25% of the area of those shims ; The material of the support pad is Q235 steel, with specifications of 160×100 —δ=16. 4.4.3 Treatment of anchor bolts and anchor plates: Oil, rust, and other contaminants on the shafts of the anchor plates and anchor bolts should be removed. Subsequently, the shaft parts should be protected against corrosion; if the instructions do not specify otherwise, apply anti-rust paint to the shaft parts twice, and apply grease to the threaded parts. Treat the contact area with the anchor plate to ensure that the horizontal deviation is no more than 2 mm/m. 4.5 Installation of the compressor unit 4.5.1 Lifting, positioning, and alignment of the unit 4.5.1.1 The turbine is designated as the reference machine for the compressor unit; during installation, the lower casing of the turbine should first be positioned and fixed, after which the other machines are adjusted and fixed using its axis as a reference ; 4.5.1.2 Before lifting, clean the lower surface of the machine base. Use a punch to mark the longitudinal and transverse center lines of the machine body at the edges of the base. Adjust the elevation of the shims and place them on the foundation as required. Lubricate the set screws and thread them out about 10 mm above the surface of the base. 4.5.1.3 Slowly lift the machine base into place so that the vertical and horizontal centerlines on the base align with the centerline on the foundation. Use shovels and jacks positioned around the unit to adjust the center position, and use the prepared shims and base set screws to adjust the elevation ; 4.5.1.4 Lift each machine into place, and use a strip level to check the longitudinal and transverse levelness of the machine body on the specially prepared surface provided by the manufacturer; the overall deviation should meet the following requirements: (1) The center line of the machine unit should coincide with the center line of the foundation, with a deviation not exceeding 5 mm ; (2) The installation elevation deviation of the reference machine should not exceed 3 mm ; (3) The allowable deviation in longitudinal levelness at the installation reference point of the reference machine should be 0.02~0.05 mm/m; for other machines, it is necessary to ensure compliance with the coupling alignment requirements ; (4) The deviation in the lateral levelness of the unit should not exceed 0.10 mm/m, and the levelness of corresponding points on the same machine should be essentially consistent ; 4.5.1.5 Once alignment is complete, tighten the foot bolts and carry out one grouting operation. (1) Make a temporary formwork around each base plate ⑸ and its anchor bolts ⑶. These templates must be firmly fixed to prevent mortar from escaping. Leave at least 100 mm of space between the inner wall of the template and the edge of the footplate. (2) As shown in Figure 3, fill the bolt holes and formwork with grouting material. To prevent bubbles from forming, the mortar must be stirred. (3) When it is confirmed that the mortar has reached the required firmness (2–3 days after grouting, but not exceeding 8–10 days, depending on local atmospheric conditions), the adjustment bolts (2) should be loosened symmetrically. (See Figure 3). (4) After the mortar has dried (depending on the temperature). In summer, it usually takes 8 days to remove the adjustment bolts ⑷ and symmetrically tighten the foot bolts ⑶. (5) Recheck the leveling. Use the adjustment bolts to adjust the shims between the base plate and the footplate ⑸ for final calibration. (6) The final alignment of the unit shall be carried out in accordance with the procedures described in 4.5.3 and 4.5.5. 4.5.5. Aligning the units concentrically (1) Alignment: Use a dial indicator to initially determine the concentrality of each machine with respect to the turbine; adjust it using the set screws on the base. The alignment values should meet those specified in the manual, and after alignment is complete, tighten the foundation bolts. 4.5.6. Secondary grouting of the unit: 4.5.6.1 Use non-shrinkage cement for the secondary grouting layer; a fitter should be present during the grouting process, and excessive vibration must be avoided to prevent displacement of the unit. 4.5.6.2 Before performing the initial secondary grouting, check and re-measure the following items and keep records: (1) The alignment deviation of the couplings and the axial distance between their end faces must meet the specified requirements ; (2) Re-measure the clearance values of the sliding pins, vertical pins, cat claws, and connecting bolts in various parts of the unit ; (3) Check whether all foundation bolts are tightened as required ; (4) If shims are used for installation, after the inter-layer tack welding is completed and the unit passes re-inspection, grouting must be carried out within 24 hours; otherwise, re-inspection shall be conducted again. (5) Before the second grouting, remove any oil stains from the surface of the foundation, rinse it thoroughly with water and keep it moist for more than 12 hours; remove any water on the surface during grouting. 4.5.6.3 During grouting, the ambient temperature should be maintained above 5°C ; The pouring must be completed in one go, and compaction should be carried out continuously during grouting to ensure that the concrete fills all areas tightly. 4.5.6.4. After secondary grouting, proper curing must be carried out; when the ambient temperature is below 5°C during the curing period, anti-freezing measures should be taken. 4.6. Installation of the ammonia compressor unit (aligning the booster and gearbox with reference to the turbine and ammonia compressor) 4.6.1. Lifting and positioning of the various machines in the unit: Clean the lower surfaces of the bases of the turbine, ammonia compressor, and gearbox. Use a marker to mark the longitudinal and transverse centerlines on the edges of the bases. Lubricate the set screws and screw them out by 10 mm, then lift the bases of the turbine, ammonia compressor, and gearbox into place (if they share a common base, lift them as a single unit). Ensure that the longitudinal and transverse centerlines on the bases align with the centerline on the foundation. Measure the distance between the shaft ends, and use jacks positioned around the unit to adjust their elevation ; A strip level is used to check the vertical and horizontal alignment at the bases of the turbine, ammonia compressor, and gearbox; the alignment is adjusted using the set screws on the bases, and once aligned, the foundation bolts of the bases are tightened. The overall deviation shall meet the following requirements: (1) The center line of the unit shall be aligned with the center line of the foundation, and the deviation shall not exceed 5 mm ; (2) The installation elevation deviation of the reference machine should not exceed 3 mm ; (3) The allowable deviation for the longitudinal levelness at the installation reference point of the reference machine should be 0.02~0.05 mm/m; other machines must meet the coupling alignment requirements ; (4) The deviation in the lateral levelness of the unit should not exceed 0.10 mm/m, and the levelness of corresponding points on the same machine should be essentially consistent ; 4.6.2 Initial alignment of the turbine and ammonia compressor: Lift the turbine and ammonia compressor into place, measure the vertical and horizontal levels of the units, and use the set screws on the base to make adjustments; once aligned, tighten the foundation bolts. 4.6.3 Secondary alignment of the turbine and ammonia compressor: A level is used at the shaft journals to check for longitudinal levelness; thin shims are employed at the support points of the turbine and ammonia compressor to adjust the vertical position of the compressor. Horizontal adjustment screws at the support points are used to fine-tune the horizontal alignment of the turbine and ammonia compressor, so that their concentricity and levelness meet the requirements for the final alignment of the entire unit. 4.6.4 After the second alignment, formally tighten the bolts at the feet and the lateral adjustment bolts and lock them, then close the upper bearing cover. 4.6.5 Alignment of the booster, gearbox, and turbine for concentricity (2) Fine alignment: Thin shims with a thickness of 0.02–4 mm are inserted between the supports of the booster and gearbox and the steel base in order to make adjustments, so that the requirements of the unit’s alignment curve in the cold state are met. The alignment values must conform to those specified in the manual; once alignment is complete, the foundation bolts of the unit should be tightened properly. 4.6.6 Shaft alignment of the unit: 4.6.6.1 The shaft alignment of the unit should be carried out after the upper and lower parts are assembled but before secondary grouting is performed. During alignment, make the adjustment using the cold-state alignment requirements provided by the manufacturer. 4.6.6.2 For the cold alignment of the unit, the three-gauge alignment method is recommended. During alignment, shaft alignment is adjusted using the already fixed turbine as a reference. Use the adjustment shims under the machine base to make the final fine adjustment to the compressor’s vertical height. Adjust the horizontal position using the lateral adjustment screw at the support. When adjusting the support shims, first support the compressor’s flexible supports with jacks, then loosen the bolts that hold the fixed support ends in place. Use the adjustment screws on the supports to lift the compressor in order to make the necessary adjustments to the shims. After making the adjustments, loosen the adjustment screws. To ensure that there is no movement in the horizontal direction, use a dial indicator to monitor the left and right supports during the adjustment process. 4.6.6.3 The shaft alignment of the unit shall meet the requirements specified in the technical documents, with an allowable deviation of generally ±0.02 mm. 4.6.6.4 When the compressor and turbine are finally aligned, fix the casing at the same time, and tighten the support bolts symmetrically and evenly one by one. When tightening the support bolts, check the shaft alignment at regular intervals; after the support bolts are tightened, recheck the shaft alignment (it should fully meet the requirements for alignment in the cold state). 4.6.6.5 When assembling the spacer sleeves of the coupling, they should correspond to the positioning marks of the coupling, and the connection bolts should match the marks on the bolt holes of the coupling. After assembly, a clearance should be left in the axial direction as specified in the technical documents; the allowable deviation is +20 mm. 4.6.7 Grouting of the unit (see section 4.5.6 of this document for details). 4.7. Treatment of the bearing housings, oil tanks, oil coolers, and oil filter elements of the compressor unit. 4.7.1 First, check the protective paint on the housings; any paint of poor quality must be removed completely ; Do not remove the top layer of the tank, as this will cause rusting due to the lack of oil exposure; however, any peeling paint on the top layer should be removed. After that, clean the tank with kerosene or gasoline, then wipe it clean with flour. Seal the entrance, take out the oil filter element and store it properly, and replace it in the filter with a temporary filter screen with a mesh size of 120–200. If the oil cooler core is severely rusted, it should first be degreased using carbon tetrachloride or trichloroethylene, and then immersed repeatedly in kerosene or gasoline until a metallic luster appears. After the oil cooler has been cleaned and found to be satisfactory, the water chamber is tested with water and finds to be satisfactory; the oil chamber is tested with oil and finds to be satisfactory. After that, it is reinstalled along with the valve components. 4.9. Unit pin positioning: 4.9.1 After the machine is aligned, fix the machine’s leg shims to the supports. 4.9.2 Adjust the clearance of the coupling bolts according to the clearance specified in the installation diagram or instructions. 4.9.5 Grind the positioning keys according to the clearance indicated in the base diagram (the total clearance should be 0.02~0.12 mm), and finally weld the positioning keys as well as the gasket plates of the positioning groove plates firmly to the base. 4.10. Stress-free piping for the unit: After the couplings of the machine have been aligned, the pipes connecting to the unit should have their fixing welds located away from the unit. The length of the straight sections at the unit’s inlet and outlet should meet the requirements specified in the drawings. Additionally, appropriate pipe supports and hangers should be used to ensure that the unit does not experience any external forces. The maximum torque of the coupling bolts at each flange of the unit must not exceed the values specified in the manual. During piping installation, a fitter shall use a dial indicator to monitor the concentricity at each coupling of the machines, ensuring that it remains within the range specified in the manual or relevant standards. The dial indicator should also be placed in a convenient location on the foundation, or on a structure that is not connected to the machine, with the probe of the micrometer pressed against the machine housing. The allowable deviations for flange connections are as shown in the table below: Rotational speed (r/min), Flange surface parallelism (mm), Radial displacement – 3000–6000: ≤0.15, ≤0.50; >6000: ≤0.10, ≤0.20. 5. Quality assurance measures: 5.1 Organize the construction crew to study carefully the drawings, regulations, standards, domestic and international standards, instructions, as well as construction procedures and methods, in order to ensure the quality of unit installation. 5.2 Strictly control the “five key stages”: drawing review, preparation of construction plans, inspection of raw materials and equipment, quality inspection of construction processes, and quality assurance for the completion deadline, so that the quality responsibility system is implemented in all departments throughout the entire construction process. 5.3 On-site, dedicated quality inspectors are assigned to oversee quality control throughout the entire installation process of the unit, ensuring strict adherence to quality standards; work from one stage shall not proceed to the next if it does not meet the required quality criteria. 5.5 Supervise the work team to carry out construction strictly in accordance with the instructions, construction plans, drawings, as well as relevant regulations and standards. 5.6 Argon arc welding shall be used for all pipes in the unit’s oil system to improve cleanliness inside the pipes and reduce the oil circulation time. 5.7 Use strength-stable, non-shrinking cement paste to grout the compressor base in order to ensure the quality of the grouting. 5.8 Quality control points for compressor installation Sequence Number Inspection Item Inspection Level Sequence Number Inspection Item Inspection Level 1 Inspection of equipment and material handover AR 8 Internal cleanliness A 2 Inspection of equipment foundation handover BR 9 Rotating the machine to check its condition C 3 Grouting of the anchor bolt holes AR 10 Monitoring of foundation settlement CR 4 Alignment of the equipment AR 5 Secondary grouting B 6 Gaps after disassembly, inspection, and reinstallation BR 7 Alignment of the coupling: before and after piping AR 6 Safety and technical measures 5.1 Before installation, safety and technical instructions should be provided to all personnel involved in the construction; these workers must be familiar with the installation procedures, operating guidelines, precautions, and emergency response measures. 5.2 Construction workers must wear safety helmets when entering the site, and safety belts must be worn when working at heights; it is strictly prohibited to work while under the influence of alcohol. 5.4 Safety assurance system (see next page) 7 Emergency response plan: In the event of an accident at the site, personnel should be immediately mobilized to carry out rescue efforts, and 120 should be called promptly. The injured should be taken to the hospital for treatment as soon as possible. The accident scene must be preserved, and an investigation into the incident should be conducted along with appropriate actions to restore normal construction activities at the site. 8. Labor Force Composition Serial Number Job Title Number of Personnel Peak Period Remarks 1 Project Leader 1 1 2 Technician 1 2 3 Material Handler 1 1 4 Maintenance Worker 1 1 5. Safety Officer 1 1 6 Electrician 1 1 Must hold a valid license 7 Welder 1 3 Must hold a valid license 8 Crane Operator 2 4 Must hold a valid license 9 Fitter 6 10 Laborers 5 5 11 Total 20 29 (Safety Assurance System) (Quality Assurance System) Serial Number Name Specification Unit Quantity 1 Theodolite Set 1 2 Dial Indicator Piece 8 3 Magnetic Base Piece 8 4 Lever Gauge Piece 6 5 Inside Diameter Micrometer 50-600mm, 0.01mm Piece 3 6 Strip Level 150mm, 0.02mm/m Piece 6 7 Iron Level 300mm, 2mm/m Piece 6 8 Frame Level 200mm, 0.02mm/m Piece 3 9 Vernier Caliper 300mm, 0.02mm Piece 3 10 Depth Gauge 0~300mm, 0.02mm Piece 3 11 Outside Diameter Micrometer 0~25mm Piece 3 12 Outside Diameter Micrometer 200~225mm Piece 3 13 Outside Diameter Micrometer 100~125mm Piece 3 14 Inner Hex Key Set 16 pieces/set Piece 5 15 Grinder φ100 Unit 5 16 Hand Chain Hoist 5T Unit 4 17 Hand Chain Hoist 2T Unit 6 18 Hand Chain Hoist 3T Unit 3 19 Gasoline kg 80 20 Kerosene kg 80 9. List of Construction Tools and Materials 1. Overview 2. Basis for Preparation 3. Conditions and Preparatory Work Required Before Construction 4. Construction Procedures, Methods, and Technical Requirements 5. Quality Assurance Measures 6. Safety Technical Measures 7. Emergency Safety Plans 8. Labor Force Composition