When using a differential pressure transmitter level gauge (Siemens) to measure liquid level, why does the gauge display a negative value when the liquid level exceeds the upper flange? Does the gas phase affect the level gauge?
Reply #22012-07-06
Either you are using a pressure guide tube, and the liquid has entered the upper end of that guide tube! ! ! !
Reply #32012-07-06
The gas phase definitely has an impact, as the pressure acting on the diaphragm is related to the density of the medium; when the density in the gas phase increases, the negative pressure becomes greater than the positive pressure, so a negative value will definitely be displayed!
Reply #42012-07-06
Of course, it’s the liquid that enters the pressure guide tube; as a result, the pressure in the negative pressure chamber increases, which is why negative pressure is indicated
Reply #52012-07-07
It’s possible that the range setting is incorrect. For a negative pressure system connected to the gas phase, it’s necessary to fill it with water first, and then adjust the range to a value between negative and 0. That should work. This is how we handle the liquid level in our boilers. Balance vessel used
Reply #62012-07-07
I find it a bit far-fetched – why can it be determined that the density is higher in the gas phase than in the liquid phase? Could you explain it in detail?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.