When using a differential pressure flow meter with an orifice plate to measure steam flow, how does one determine the small-signal cut-off value?
Reply #22012-07-16
This post was last edited by supersuboy on 2012-7-20 08:22. Small-signal rejection is required, for example, 5% rejection. It can be achieved through modification; protocols that support Hart can be modified using a handheld controller
Reply #32012-07-16
What was said upstairs is correct; 5% is a suggested value, and this value can also be determined based on the specific conditions of the operation.
Reply #42012-07-16
When using an orifice plate to measure steam flow, how should the small-signal cut-off value be selected?
Reply #52012-07-16
This post was last edited by hjbjl on 2012-7-17 15:11. Strongly oppose the notion of \"interference\". . . Question: Is low-temperature signal rejection available? Can low-pressure signals be removed? Is small-signal current rejection available? Can low battery signal clipping be enabled? . . . . . . . . . Is it perhaps because of the special nature of traffic that interference occurs and monopolies arise? ! Is it perhaps because of the special nature of traffic that interference occurs and monopolies arise? ! Is it perhaps because of the special nature of traffic that interference occurs and monopolies arise? !
Reply #62012-07-16
Since flow rate is proportional to the square root of the differential pressure, if the differential pressure is 2%, then the flow rate will be √2% = 14.14%. Therefore, when the flow rate is very low, errors in the flow rate indication can be significant due to the errors in the differential pressure gauge.
Reply #72012-07-16
The small-signal cut-off for orifice plate flowmeters should be as low as possible; we generally use 1%.
Reply #82012-07-17
Why use an orifice plate for measurement? Isn’t a vortex flow meter better? ? ?
Reply #92012-07-20
1. “A differential pressure of 2%” corresponds to a flow rate of “√2% = 14.14%”. This is not an issue related to measurement errors in the differential pressure gauge! Rather, the use of the mathematical relationship √2 is overly forced, which leads to severe distortion in the amount of computation required for low-flow, low-signal conditions, and poses a serious theoretical flaw 2. Small-signal trimming is an engineering approach taken when the errors are too large to be resolved properly, forcing rough compensations; it is an unsightly method that lacks mathematical modeling support. 3. After decades of practical application, there have been endless debates and numerous problematic cases; this approach lacks depth and sophistication in thinking, relying on conventional methods. How can precise measurement be achieved in such a situation? ? ? ? ? ? It can only be a game, a dream – an illusion and delusion. In the 2010s, instrument designers and instrument application engineers, you all hold master’s and doctor’s degrees; you ought to have a moral and scientific responsibility to re-examine and reassess certain measurement theories 4. To provoke further discussion: Russia is nothing but a worthless, contemptible country. In my opinion, the relationship between pressure difference and flow rate should at least be redefined and studied using a polynomial formula: Y=A0+A1X+A2X^2+A3X^3
Reply #102016-08-22
√Can the equation 2% = 14.14% hold?
Reply #112016-08-23
The differential pressure transmitter, which supports HART, can be isolated at the gauge head or within the DCS system.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.