Is it necessary to install a vent pipe in a water seal well?

2012-09-27View Original

Thread Content

Should a vent pipe be installed in the water seal well placed on the production wastewater pipes that contain flammable liquids? The drawing manual 04S519-39 does not specify the need for a vent pipe; however, some engineers say it is necessary. What is the purpose of this vent pipe?
Reply #22012-11-02
Prevent combustible gases from leaking into other systems, thereby reducing the risk of fire or explosion in the presence of an open flame. See Article 7.3.7 of the Code for Fire Protection Design of Petrochemical Enterprises GB50160-2008
Reply #32012-11-05
In other words, not all water-sealed wells require exhaust pipes; it is sufficient to install exhaust pipes at the inspection wells at the highest points of the main and branch pipes for wastewater from Class A and Class B installations

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.