For combustible gas concentration alarms, there are two DI points: a high alarm and a very high alarm (a concentration of 20% triggers the high alarm, while 40% triggers the very high alarm). When this is integrated into the PLC system, is it necessary to use 1 DI card or 2 DI cards?
Reply #22012-12-24
DI card? Is it an expansion module? One is enough; there should be at least over 2 DI points.
Reply #32012-12-24
Does your combustible gas detector have two alarm outputs? If it has two alarm outputs, then two DI points are required; if it has a 4–20mA output, only one AI point is needed. The alarms are implemented through point configuration. The alarm threshold for combustible gas concentration is generally above 60 LEL; 20 LEL is too low
Reply #42012-12-24
Flammable gas concentration alarms generally provide digital output, with two separate switch circuits that are fed into the corresponding DI modules of the PLC; 2 DI channels are required. DI modules generally have 8, 16, or 32 channels, so one module is sufficient.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.