2007-12-16View Original

Thread Content

Today I conducted a manual trip test. With the machine not started and no steam supplied, only the auxiliary turbine oil pump was turned on. Once the oil pressure reached the normal level, I performed a manual trip; the emergency shutdown device activated and the main steam valve also closed, but the control valve showed no reaction at all! It’s very frustrating – I don’t know what’s going on
Reply #22007-12-16
Please have the original poster carefully inspect the oil circuit of the control system to check for any leaks. If the main valve moves, it indicates that there is no problem with that oil line; if the control valve does not move, then there must be a leak somewhere, as the pressure is not sufficient to allow the high-pressure oil to reach the actuator, and therefore the control valve will not move either.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.