2007-12-18View Original

Thread Content

Our company has newly set up an ice machine production line. During pressure testing, an air compressor is used to apply pressure, and a washing powder solution is used to test each flange connection. Small bubbles always appear at the flange connections. Asbestos gaskets are used for these connections. I have checked carefully and the installation is correct; perhaps there is something wrong with the method of pressure testing. I would be very grateful if someone could tell me the reason
Reply #22007-12-18
There’s no issue with the pressure testing method. You say that the installation is fine; or maybe it’s necessary to disassemble it and replace the gaskets. I think it’s still an installation problem. If that doesn’t work, check whether there are any quality issues with the flanges – they have holes
Reply #32007-12-19
Asbestos gaskets should have been phased out long ago – why is someone still using them in cooling systems?! Agree with the person above; replace the gaskets first and then conduct a leak test. However, don’t forget to check for leaks at the welds and joints during the test.
Reply #42007-12-19
1. Asbestos gaskets should not be used; the gaskets provided on the third floor can be used instead. 2. Check whether there are any issues with the flange sealing surface. 3. 704 can be considered for coating on the gasket
Reply #52007-12-19
If bubbles appear, there is definitely a leak; replace the gasket, and make sure to maintain a uniform tightening torque on the flange bolts
Reply #62007-12-19
Your suggestions have been very helpful to me; thank you!
Reply #72007-12-19
Leaks can also occur within the asbestos itself.
Reply #82007-12-20
I think it’s a gasket issue; the gasket should be replaced, such as PTFE
Reply #92007-12-21
Asbestos gaskets have problems and cannot be used in refrigeration equipment

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.