Vibration of the lockbox flushing pipeline

2007-12-22View Original

Thread Content

When our lockhopper has finished discharging slag and the slag discharge valve is closed, there is a very loud banging sound coming from the wash water valve and its pipelines; I’m not sure what the cause is. This post was last edited by Langtaosha on 2008-3-14 at 11:05
Reply #22007-12-22
Is it related to the speed at which the slag discharge valve is opened and closed? You can try adjusting the rate
Reply #32007-12-22
It is estimated that the impact on the equipment and pipes was caused by the flushing water from the lock hopper washing the lock hopper
Reply #42007-12-22
Based on experience with boiler hydraulics, it is likely that the valve was closed too quickly, causing a sudden change in the water flow rate inside the pipes and resulting in a \"water hammer\" phenomenon. Searching online should allow you to find descriptions of many types of \"water hammer\".
Reply #52007-12-22
Please refer to: http://bbs.hcbbs.com/viewthread.php?tid=49086
Reply #62007-12-22
It’s definitely the \"piston hammer\" phenomenon; the solution is to be more careful during operation and move more slowly! ! !
Reply #72007-12-23
The poster should check the pipeline from the flushing water tank to the flushing water valve; a spring joint should be installed there. It’s likely that loose bolts are causing the noise that occurs each time the valve closes after slag removal. :lol
Reply #82007-12-23
Is it possible that the noise is caused by resonance? Eliminating the source of that resonance will solve the problem. Resonance can sometimes be highly destructive
Reply #92008-12-07
Is that sound the noise of flow interruption caused by the rapid closing of the flush valve? ? ? ? ? If you don’t believe it, you can give it a try; remember to use a ball valve?
Reply #102008-12-07
This phenomenon is very common in Texaco systems; it is mainly caused by water hammer. The only solution is to reinforce the pipelines. As for any good methods, I hope everyone will actively discuss them

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.