HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Strangely, the gas electric gate valve in our plant closed on its own. Please help me figure out what could be the reason

2007-12-24View Original

Thread Content

I work in the recycling workshop at a coking plant. Yesterday, one of the gas-operated valve switches in my workshop closed on its own, resulting in significant gas leakage. When the operator tried to turn it on, it closed again on its own; this happened twice before it finally stopped working. The electrician was unable to identify the cause. I hope some experts can help me out
Reply #22007-12-24
I work in the recycling workshop at a coking plant. Yesterday, one of the gas-operated valve switches in my workshop closed on its own, resulting in significant gas leakage. When the operator tried to turn it on, it closed again on its own; this happened twice before it finally stopped working. The electrician was unable to identify the cause. I hope some experts can help me out
Reply #32007-12-24
The on and off buttons are interlocked through the normally open and normally closed contacts of the contactor control coil. Based on what you’ve described, it seems that there is a problem with the off button (it may not reset properly, causing it to stay in the on position). When the button is pressed to turn on the device, the normally closed contact of the contactor control coil breaks, thereby cutting off the circuit that controls the off function. However, once the button is fully pressed, the limit switch comes into action, cutting off the circuit that allows the valve to open; at the same time, the contactor contacts return to their normal closed state, and the motor stops rotating. After the off contact of the AC contactor coil returns to its closed state, if the off button is still in the on position, the off circuit will be activated, resulting in automatic shutdown.
Reply #42007-12-25
Personally, I think it’s not due to mechanical reasons; it’s most likely an electrical issue. Could it be caused by humidity leading to a short circuit? The actuation mechanism of the electric gate valve should not be able to close under the effect of gravity. It would be best to have someone with electrical expertise take a closer look; if that doesn’t work, then the electrical control system needs to be replaced.
Reply #52007-12-25
It might be due to electrical control issues
Reply #62007-12-25
It must be a problem related to the electrical system. For important gas-powered gate valves, it is normal for them to lose power during normal operation; it makes more sense for them to close while still powered on. By checking the electrical aspects, one can figure out what’s going on.
Reply #72007-12-25
If the electrician determines that the cause cannot be identified, and a self-protection system has been installed, have the instruments checked
Reply #82007-12-25
Is it an electrically closed valve or an electrically open valve? Did it suddenly receive power again for some electrical reason, when it should have been powered off? Or the opposite?
Reply #92007-12-25
Thank you all. After two days of investigation, it was found that the cable’s outer coating was damaged during installation; over time, and especially at night when humidity is high, this led to a short circuit, which caused the problem. . . .
Reply #102007-12-26
Open the junction box to check if water is entering
Reply #112009-02-28
Why isn’t a pneumatic single-acting disc valve used for the gas supply valves? It operates quickly and can close automatically in the event of a power outage. I have a suggestion – I hope everyone can give some advice
Reply #122009-02-28
It’s due to electrical control issues; we’ve encountered similar situations here as well, and it’s probably caused by a loss of power to the solenoid valve.
Reply #132009-02-28
Could it be that the pipeline is vibrating, causing the valve core to fall out?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.