I currently have a pressure switch with dry contacts, whose contact rating is AC250V 5A/DC30V 5A. The location where it is installed is a non-explosion-proof area. My question is: can the signal from this location be connected directly to the DCS cards? Is relay isolation required?
Reply #22008-01-17
Dry contacts can be connected to DCS cards without any problems generally; most factories connect dry contacts in this way these days, without the need for relay isolation, and it’s fine even if the site is not a explosion-proof area.
Reply #32008-01-17
Connect directly, no isolation needed: lol :lol
Reply #42008-01-17
If it is confirmed that there is no interference from strong voltage signals, it can be connected directly.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.