When using a 2500KVA dry-type transformer, what size circuit breaker should be chosen?

2008-02-28View Original

Thread Content

Should we choose a frame current of 4000A or 5000A, with the current set at 4000A?
Reply #22008-03-04
It is best to use a 5000A frame; a 4000A switch does not provide sufficient stability in operation.
Reply #32008-03-04
5000A should be selected, with the setting adjusted to 4000A. Generally, for a 2000KVA transformer, 4000A is chosen, with the setting adjusted to 3200A.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.