I have been working in this field for many years, but I have never found any specifications that clearly state the settings for tank liquid levels; everything relies on empirical methods. I don’t know which specification it’s in? Including high level alarm, over-high alarm, low level alarm, and under-low level alarm. Last edited by chinazwr on 2009-3-23 18:34.]
Reply #22008-07-09
Generally speaking, both high-high alarms and low-low alarms indicate situations where an accident is likely to occur. For ordinary liquid tanks, if the normal filling coefficient is 0.9, you can set a range of 0.92–0.93 as the value that triggers a high alarm; a high-high alarm can be set at 0.95–0.96, meaning that values above this range may lead to an accident. Pre-planned measures must be taken immediately ; A low alarm occurs when, for example, the flow rate of a pump is maintained at 10–15 minutes; if it drops below 5 minutes, immediate action is required. In such cases, it’s considered a very low alarm – meaning effective measures must be taken within 1–2 minutes, otherwise an accident will occur
Reply #32009-03-23
What is the OP’s specialty? A specification for oil storage tanks in the petrochemical industry requires the installation of high-level switches, but low-level switches are not mentioned and therefore need not be installed.
Reply #42009-03-23
A high liquid level switch can be installed, but a low liquid level switch is not necessary!
Reply #52009-03-23
The maximum liquid level in the storage tank is 85% of its capacity (90% for tanks with internal floating roofs); this can be found in the tank design specifications. High and low alarm settings can be calculated based on the feed (discharge) volume, in accordance with a certain time frame for handling incidents.
Reply #62011-01-14
It’s necessary to have a low-level alarm, right? If it gets emptied, the consequences can be severe – for example, high-pressure fluid from the hydrogenation unit could flow into the low-pressure section, such as from the high-pressure stage to the low-pressure stage, or directly from the reactor to the low-pressure section.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.