The meaning of FC marked below the control valve for separator interface adjustment in PID

2008-10-09View Original

Thread Content

I would like to ask what FC means, which is indicated next to the control valve used for adjusting the separator interface in a PID system? Some say it’s flow control, while others say it’s an emergency shutdown – what exactly is it?
Reply #22008-10-09
The so-called deflation valve is the gas opening valve, with a positive effect. .
Reply #32008-10-09
What was said on the 2nd floor is correct – it means that even when the instruments malfunction, the valve can still remain closed
Reply #42008-10-09
FC stands for the initial letters of Flare Close.
Reply #52008-10-09
Thank you. At least I know it’s not traffic control
Reply #62008-10-09
FC: Fail close – the control valve closes in the event of an interruption or failure in the instrument air supply. That is, the gas control valve operates in fail-open mode: it opens when the instrument air supply is interrupted or fails. That is, the air shut-off valve FL: Fail Lock – when the instrument air supply is interrupted or fails, the control valve remains in its original position
Reply #72008-10-09
Fail close. Air-shut off means the air valve opens
Reply #82008-10-10
Fail Close: Failure-induced shutdown; it is a pneumatic-operated valve and functions as an emergency shut-off device!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.