Keywords of this article: Rosemount transmitters http://china-rosemount.cn/ Rosemount transmitters fail to communicate with the handheld controller. Solutions: a) Check the power supply voltage of the transmitter; b) Check the load resistance (*minimum 250 ohms) ; c) Check whether the transmitter address is correct ; d) Replace the electronic circuit board. 7.3 The 7.3 milliampere reading is low or high. Action to take: a) Check whether the pressure variable reading is saturated ; b) Check whether the output is in an alarm state ; c) Perform 4-20mA output trimming (Output Trim) ; d) Replace the electronic circuit board. 7.4 No response to changes in applied pressure. Action taken: a) Check the testing equipment ; b) Check whether the pressure tap pipe is blocked ; c) Check whether range adjustment is not possible (rendering the range adjustment function inoperative) ; d) Check the transmitter’s protection function jumper switch ; e) Verify setting of calibration points (4 and 20 milliamps) ; f) Replace the sensing diaphragm. 7.5 Low or high readings of the pressure variable: Action taken: a) Check whether the pressure tap is blocked ; b) Check the testing equipment ; c) Perform full sensor trimming ; d) Replace the sensing diaphragm head. Shanghai Mengyan Automation Equipment Co., Ltd. Address: Room 1119, Jiahong Building, No. 639 Guangfulin Road, Songjiang, Shanghai. Contact person: Xu Gong. Mobile phones: 18616582302 / 18616582330. QQ: 764861476. Email: sales@shmyzdh.com