SIEMENS PS2 positioner: the valve oscillates repeatedly, how to solve it?

2008-12-04View Original

Thread Content

We have been using domestic positioners; recently, while servicing a SIEMENS smart positioner, we found air leakage at the connection point leading to the positioner, located after the air pressure reducing valve. Is this the direct cause of this fault? ? ? Since the valve cannot be cut out, it can only be repaired online. It is manifested as: DCS set to manual mode, output at 65%, with the feedback fluctuating between 63% and 67%. The pressure indicated by the manometer on the pressure relief valve oscillates, vibrating intermittently at 3.5 bar. Even the domestic positioners I use have air leakage issues; it shouldn’t be this bad.
Reply #22008-12-04
Isn’t there a duplicate line for the installation of control valves? It can be switched to manual control on the double-track system for maintenance
Reply #32008-12-04
There is air leakage at the connection point of the positioner behind the air supply pressure regulator, and this is likely the main cause of the oscillations. Intelligent positioners have very strict requirements regarding the air supply Domestic mechanical positioners are relatively inferior! :)
Reply #42008-12-04
Try lowering the sensitivity in the configuration menu; it’s likely a fault in the amplifier’s gas circuit, which probably needs to be cleaned.
Reply #52008-12-04
The control valve does not have a double line; it is the inlet guide vane of the compressor. Excuse me, on the fourth floor, how do I adjust the sensitivity?
Reply #62008-12-04
My opinion is the same as that on floor 4; the method for adjusting sensitivity is listed in the instructions!
Reply #72008-12-04
Is it being debugged online? It really can’t be repaired in that way. Is there any danger in debugging online? 1. Is the sensitivity a bit too high, meaning the dead zone is too small? It should be increased. 2. It’s probably not a problem with air leakage at the connection points; to check this, increase the air supply and see if oscillation still occurs. 3. Is there any air leakage in the actuator? This post was last edited by Big Face Cat on 2008-12-4 at 19:47
Reply #82008-12-04
Don’t move it online; the guide vanes have a significant impact, and any movement will cause the air compressor to stop. Other systems will also be affected. Wait until maintenance can be carried out.
Reply #92008-12-04
For the SSIEMENS SIPART PS2 locator, select option 34.DEBA: the control dead zone ranges from 0-100%, and the sensitivity can be adjusted
Reply #102008-12-04
Think about it; it definitely has nothing to do with the air compressor.
Reply #112008-12-04
The 5th floor says it’s the compressor impeller. The person in charge of the 5th floor and the 1st floor must be the same person. Last edited by ddfly on 2008-12-4 20:18.]

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.