Inspired by members from other forums, and as I myself need experience in this area, I am seeking regulations and guidelines. The details are as follows: Since different petrochemical companies have distinct characteristics, there are also various regulations. Therefore, I would like to collect the management regulations for instrument workshops and teams from various companies, so that everyone can learn from them. Please feel free to participate actively. The specific requirements are as follows: 1. Collect regulations and requirements regarding instrumentation technology, management of instrumentation equipment, and labor discipline for instrumentation personnel; submissions that are not related to the above shall not be sent. 2. The regulations and requirements collected must be complete and organized. 3. There are no limits on the number of entries or their length for participants. 4. Please do not include the company name in the issued regulations and requirements; other symbols can be used instead. Everyone is encouraged to participate. If a post meets the requirements, please give it a higher score as a reward. :D :D
Company’s Management System for Interlock Protection Systems in Instrumentation 1. Interlock protection systems are managed at different levels depending on their importance. 2. When changes are required (including set values, interlock procedures, interlock methods, etc.), or when the interlock protection system is to be disabled or cancelled, formal procedures must be followed. When disabling the interlock protection system, corresponding preventive measures and remediation plans should be established. 3. When performing tasks such as making changes to the interlock protection system, temporarily or permanently disabling it, or canceling its functions, an interlock protection system work order must be prepared, specifying the basis for the task, the person responsible for carrying out the task/supervisor, the details of the tasks to be performed, and the time of execution. 4 Before putting new installations or equipment into operation after maintenance, and before restoring interlock protection systems that have been disabled for an extended period, all interlock circuits must be thoroughly inspected and verified. The verification of the interlock circuit should be carried out with the participation of relevant professionals; after the inspection and verification, an interlock circuit verification form (sheet) should be filled out. 5. The components used in the interlock protection system (including primary sensing elements, circuits, and actuating elements), as well as the computing units, should be inspected, calibrated, and adjusted during the shutdown and maintenance of the device. Newly replaced components, instruments, and equipment must be inspected and calibrated before they can be installed in the system. After maintenance of the interlock protection system, calibration must be performed. 6. The newly added interlock protection system must come with complete drawings and documentation. 7. To prevent misoperations, supervised operation must be carried out when performing tasks to disable or restore interlock circuits. Close communication should be maintained with the process operators during operation. After processing, it must be detailed and signed for confirmation on the interlock work order. 8. The panel switches and buttons of the interlocking system are all operated by the operator ; The post-market switches and buttons are operated by the instrument crew. 9. All emergency stop buttons shall be equipped with reliable guards. 10. The interlocking protection system should have sufficient spare parts. 11. The maintenance and repair of instruments in the interlock protection system shall be carried out in accordance with the requirements of SHS 07007-2004, \"Procedures for Maintenance and Repair of Petrochemical Equipment\".
Company’s Professional Production Management System for Instruments: This system covers aspects such as production shift duties, routine inspections of instruments, overtime work in production, and emergency repairs during production. Chapter 1: Production Shifts Article 1: Implement the post responsibility system, strengthen the management of shift work, and ensure the long-term operation of instruments ; Article 2: Shift system adopted by the branch offices 1. Monthly rotation shifts: This means that the staff members remain fixed, working in three shifts on a monthly basis; each shift is responsible for all night shifts as well as day shifts on rest days during that month. 2. Day shift: Refers to the personnel permitted to be on duty, other than the shift leader, deputy shift leader (also acting as safety officer), and those on monthly rotation, who are responsible for the day shifts on non-rest days. Centralized duty: Refers to the practice of having the duty location and personnel concentrated at a branch office during specific periods, responsible for monitoring instruments within that branch office. 3. Daily shift rotation: refers to the duty shifts covered by the branch managers. (24-hour duty) 4. Long shift: Refers to the system in which the team arranges for the available staff to take turns on duty during the day and at night. Article 3: The personnel assigned to duty are as follows: 1. Team duty: Those who are qualified for duty, excluding the team leader and the deputy team leader (who also serves as the safety officer). 2. Branch office duty: Branch leaders, branch management and technical staff ; Article 4: Shift hours for duty personnel: Day shift – 8:00–16:30; Night shift – 16:30–8:00. If special circumstances require adjustments to the shift hours, approval from the branch’s management is necessary. Article 5: For those on monthly shift rotation, those starting a shift work as usual on the day before, while those finishing their shift take two days off after their last shift ; The working hours of the on-duty personnel during holidays are considered overtime, and the regulations regarding such overtime are set and reported uniformly by the branch office. Article 6: Those on night shifts during regular working hours may take one day off ; One extra day off is provided for working on rest days. Those on the long shift can take a break on the afternoon of their night shift and take over at the designated time. Each team shall arrange for its duty personnel to take their rest days within the week, as long as it does not affect work. Article 7: Duty personnel shall strictly implement the duty reporting and briefing system. The reporting time for shift crew members on night shifts at the branch office is 17:00, while for day shifts on holidays it is 8:00 ; For online production shift handovers, the daytime deadline is 16:30, and in the morning it is 7:30 ; The on-duty staff at the branch offices must report to the company by 8:30 in the morning. The deadline for submitting the shift handover online is 16:40 in the afternoon, and by 7:40 in the morning. In the event of a network failure, the situation on duty should be reported by phone. Article 8: The person handing over duties shall clean the area in advance and fill out the shift handover log. Shift handover logs must be filled out with a pen, using blue-black or pure blue ink. The writing should be in the Fangsong style, with a uniform format, neat handwriting, and detailed entries. Specific requirements: 1. The successor should conduct a preliminary check 10 minutes in advance, checking the shift handover log and tools and instruments, as well as the contents of the emergency kit ; 2. The shift handover personnel must attend the morning pre-shift meeting; they shall clearly convey information regarding production status, tools, and equipment, and the incoming personnel must verify this and sign accordingly ; 3. The person handing over the shift poses questions to the person taking over regarding job-related skills, and assigns a score based on their answers ; 4. The entries in the shift handover log must be detailed and clear, including the time, participants, instrument part numbers, cause of the fault, handling process, and results. 5. Strictly enforce the five no’s for handover: ①. Do not hand over if the tasks for the current shift have not been completed or properly explained ; ②. Incomplete log records shall not be handed over ; ③. Shift-handover shall not be carried out if the instruments, tools, and equipment required for duty are incomplete ; ④. No handover until the successor arrives ; ⑤. The duty room will not be handed over if it is not clean. Article 9: Requirements regarding the assignment of duty personnel 1. Shift workers shall not be assigned continuously ; 2. Once the shift schedule is arranged, it must not be changed arbitrarily ; 3. In the event of special circumstances that require changes to the two aforementioned duty personnel, such changes can only be made upon their own application and with the approval of the branch’s management. 4. In principle, all teams operate on a rotating shift system; in case of special circumstances, the team leader must explain the reasons and obtain approval from the supervising manager before adopting another form of shift arrangement. Article 10: Several Disciplines for Shift Work 1. Shift workers must abide by all relevant regulations. 2. The duty personnel must not go to sleep before 23:00. 3. The duty personnel must handle faults promptly and thoroughly, ensuring that issues are resolved without delay. 4. If a duty officer needs to leave temporarily for some reason, they must inform the duty dispatcher at the branch office. If there are special reasons that require leaving work early, approval from the duty officer at the branch office is necessary, and in such cases, someone else must take over the shift. 5. When duty personnel leave their post to address issues at other equipment, they must carry communication devices or inform the duty personnel at the branch office of their whereabouts. Article 11: Responsibilities of the office duty personnel: 1. Responsible for handling and coordinating various issues related to instrumentation and equipment that arise during production while on duty across the entire company. In accordance with the division of responsibilities, any major instrument issues encountered or updates regarding their handling should be reported to the branch’s management in a timely manner, or communicated with the relevant personnel in the office. 2. Responsible for supervising and inspecting the duty arrangements of various teams, their presence on duty, the handover procedures, as well as safety production and labor discipline, and providing timely feedback for evaluation purposes. 3. Responsible for completing temporary tasks assigned by company leaders and higher-level departments, and as required, seeking guidance from relevant superior departments and reporting on major issues that arise during the shift along with the actions taken to address them. 4. In the event of any emergencies during duty hours, including (fires, explosions, hazardous material leaks, poisoning incidents, power outages, failures in large-scale equipment or critical instrumentation, as well as various types of equipment failures and injuries to personnel), the \"Branch Company Emergency Procedures\" must be promptly activated, and the situation reported to the company’s dispatch center. 5. The duty personnel must report to the branch’s dispatch office by 8:30 every day. Information on the production activities during their shift is entered into the Mechanical and Electrical Company’s network management system. They are required to submit a report on the previous shift by 7:40, and a report on their own shift by 16:40. 6. During duty, if problems arise that cannot be resolved by the team members on duty, one should go to the scene personally to coordinate and handle the issues, or notify the relevant technical personnel to arrive at the scene to resolve them ; 7. Be responsible for the security of the branch office building; lock and close all the doors of the building promptly, conduct inspections to ensure the building is secure against theft, and report any abnormalities to the relevant departments immediately ; Chapter 2: Routine Inspection of Instruments Article 13: From Monday to Friday, personnel in each shift shall strictly carry out routine inspections and labeling of the instruments in their respective areas (posts) in accordance with the regulations ; and sign in the process inspection record book ; Article 14: During holidays, the on-duty personnel shall conduct inspections of the instruments in their assigned area and sign in the process inspection record book ; Article 15: Time for daily inspections and label checks: 8:30–9:30 am and 3:00–4:00 pm. Article 16: Daily inspections include special care inspections; the contents and requirements for such inspections must be carried out in strict accordance with the regulations set by the refining branch and the automation control branch. The results of special care inspections must be recorded accurately and promptly in the special care log ; Article 17: Daily inspection personnel and inspection details shall be recorded in the respective posts section of the branch’s online shift handover system ; Article 18: Contents of regular inspections: 1. In accordance with the designated inspection routes, check whether the operating condition of various instruments and equipment is satisfactory, as well as whether there are any abnormalities in parameters such as pressure, temperature, flow rate, and vibration within the system ; 2. Check the operation rates of various instruments and equipment, as well as any leaks or loose connections in the piping system; address any issues found promptly or report them, and fill out the record book for rectifying potential hazards ; 3. Maintain cleanliness in the environment surrounding the instrumentation and its systems ; 4. Check the power supply, air supply, wiring, grounding, insulation, and explosion protection of various instrument systems ; 5. Check the environmental temperature and humidity in the control room, as well as measures against rats and insects; conduct UPS discharge tests on the instruments; verify the operation, communication, alarm functions, and redundancy of the industrial computer system, as well as ensure proper data backup (with the process team handling the data backup); resolve common faults and fill out inspection records, which must be signed off by the operators from the production branch. 6. When conducting inspections, bring cleaning cloths, common tools, a multimeter, walkie-talkies, etc. Use methods such as visual inspection, listening, touching, and smelling to check the operation status of the instrumentation system, and keep comprehensive and complete inspection records ; 7. Any issues identified during inspections must be addressed promptly; those that have a significant impact on production and cannot be resolved immediately should be reported to the relevant departments without delay. Chapter 3: Overtime in Production Article 19: When employees of a branch office need to continue working outside the designated working hours due to work requirements or tasks assigned by the branch, such work is referred to as overtime. Overtime is divided into the following two types: 1. Temporary overtime: Working outside the designated hours due to production or work needs. 2. Overtime on holidays: Working on holidays due to production or work requirements. Article 20: When employees of branch companies are assigned to work overtime on holidays or outside regular working hours due to production or work requirements, they shall not refuse without special reasons; otherwise, they will be assessed depending on the severity of the situation. Article 21: For overtime hours worked due to work requirements, the overtime application form provided by the branch office must be filled out by the 28th of each month. After it is signed by the employee who is working overtime and the team leader, it shall be submitted to the branch office’s production supervisor for compilation, and finally approved with the signature of the branch office’s production director. Article 22: The standards for paying overtime allowances are as follows: 1. For temporary overtime (between noon and 23:00), an overtime allowance equal to 1.5 times the regular wage shall be paid. 2. Overtime on holidays is compensated with double wages as overtime pay. 3. For statutory holidays and overtime worked after 23:00, an overtime allowance of 3 times the regular wage shall be paid. 4. Overtime exceeding 3 hours (or in total) is counted as half a day ; Those exceeding 6 hours are counted as one day ; If the overtime time is less than 3 hours, it will be reflected in the team’s bonus. Article 23: After overtime allowances are paid, no further rest time shall be arranged; otherwise, strict penalties will be imposed. Paying individuals for overtime is included in the cost of each shift. Chapter 4: Emergency Production Repair In cases where, due to unexpected incidents such as fires, power outages, loss of air supply, lightning strikes, medium leaks, or accidents involving process equipment, all, most, or critical instruments in a production facility cease to function, preventing the facility from operating properly and posing a serious threat to safe production, Article 24 states that the production team shall immediately inform the team leader, the branch company, and the company’s dispatch department ; Article 25: In the event of a major accident that results in some of the instruments in the facility failing to function properly, the branch company shall establish a emergency repair leadership team headed by the deputy production manager, in order to promptly organize the personnel from the relevant teams to carry out repairs ; Article 26: In the event that unexpected circumstances cause a large number of instruments in the installation to become unusable, thereby preventing the production facility from operating properly, a emergency repair leadership team headed by the branch manager shall be established. Crossing team boundaries, all necessary production repair personnel, including those responsible for logistical support, shall be dispatched immediately. The extent of the damage shall be investigated right away, a repair plan shall be developed, repair measures shall be put into effect, and repairs shall commence promptly. All personnel must unconditionally comply with assignments ; Article 27: Logistics support personnel shall promptly obtain various instrument parts based on the extent of damage, and ensure provision of daily living services ; Article 28: Emergency repair personnel must pay attention to safety and complete the tasks on time within the timeframe specified by the branch ; Article 29: For the emergency repair of instruments in a critical circuit or unit, each production team shall assign sufficient personnel to develop an emergency repair plan based on the circumstances; meanwhile, the branch company shall send managers to the site to provide assistance and guidance ; Article 30: For emergency repairs such as leaks under normal circumstances, each team shall handle them on its own while paying attention to safety; after completion, they must report to the branch company ; Article 40: These Provisions on the Production Management System of the Self-Control Branch shall come into effect as of today, and the existing production management systems applicable to the Instrument Workshop shall be repealed simultaneously. Compiled by: Reviewed by:
Regulations on the Management of Instruments, Meters and Automatic Control Systems Chapter 1 General Provisions Article 1 These regulations are formulated in order to strengthen the management of instruments, meters and automatic control equipment (hereinafter referred to as “instrumentation equipment”) at XXX Co., Ltd., improve the level of management of such equipment, and ensure its safe and economical operation. They are based on relevant laws and regulations, as well as the “Equipment Management Regulations of Sinopec” and the “Equipment Management Methods of China Petrochemical Corporation”. Article 2: The main objective of instrument and equipment management is to carry out scientific management of such instruments and equipment throughout their entire life cycle – from planning, design, manufacturing, selection, procurement, installation, operation, maintenance, repair, renovation, and upgrading to eventual disposal – in order to keep them in good technical condition. Article 3: The instrumentation equipment referred to in these regulations includes various types of testing instruments, automatic control and monitoring instruments, actuators, process control computer systems, analytical instruments, combustible (toxic) gas detection and alarm devices, as well as their auxiliary units, which are used in the production and operational processes of our company. Article 4: This system applies to all departments at the company’s head office; branch companies and subsidiaries shall follow it accordingly. Chapter 2 Management Institutions and Scope of Responsibilities Article 5 Instrumentation equipment is under the centralized management of the Motorization Department. Each unit should have corresponding positions and full-time technical personnel in its equipment management department. Under the leadership of the deputy manager in charge of equipment management, the Mechanical Department is responsible for the management of the company’s instrumentation equipment. Article 6 Responsibilities for the management of instrument equipment in the Mechanical Department: (1) Implement the guidelines, policies, and regulations regarding the management of instrument equipment, as well as the company’s systems, procedures, and rules related to such equipment. (II) Organize the formulation and revision of the company’s management systems, procedures, standards, and regulations for instrumentation equipment. (III) Inspect the implementation of instrument management systems, procedures, standards, and regulations by various units. (IV) Participate in the preliminary management tasks such as planning and design selection of instrumentation equipment for key projects including new plant construction, upgrades, or technological improvements. (5) Responsible for approving the plans for the purchase of new or replacement instrumentation equipment submitted by various departments of the company, and consolidating these requests for procurement by the Supply and Sales Department; also responsible for approving the plans for the disposal of outdated instrumentation equipment as well as maintenance work on such equipment submitted by various departments of the company. (VI) Responsible for reviewing or formulating plans for technical improvement and enhancement projects related to the instrumentation equipment and systems in various departments of the company. (7) Be responsible for the daily operation and maintenance of the company’s instrumentation equipment, and compile and submit reports on the technical condition of automated instruments on schedule. (8) Be responsible for reviewing the maintenance projects and plans for the company’s key instrumentation equipment, and participate in the acceptance of such critical instrumentation projects. (IX) Responsible for organizing exchanges on new products and technologies in instrumentation equipment, as well as exchanges of management experience. (10) Participate in the investigation and analysis of major accidents involving the company’s instrumentation equipment. Submit accident analysis reports on instrument equipment in a timely manner, and urge all affiliated units to do the same. (11) Organize the establishment and maintenance of the company’s inventory records and archives for instrumentation equipment. Article 7 Responsibilities for the Management of Instrumentation Equipment in the Inspection and Maintenance Department: (1) Implement the relevant guidelines, policies, and regulations regarding the management of instrumentation equipment, as well as the company’s systems, procedures, and rules related to such equipment. (II) Participate in the preliminary management tasks such as planning and design selection of instrumentation equipment for key projects including new plant construction, upgrades, or technical improvements. (III) Submit plans for the purchase, replacement, disposal, and maintenance of instrumentation equipment to the Motor Affairs Department. (IV) Participate in technical improvement and upgrade projects for instrumentation equipment and their systems. (5) Be responsible for the daily operation and maintenance of instrumentation equipment. (VI) Participate in the maintenance projects and plans for important instrumentation equipment in the Operations Department, and take part in the acceptance work for such important instrumentation projects. (7) Organize participation in exchanges on new products and technologies for instrumentation equipment, as well as exchanges of management experience. (8) Participate in the investigation and analysis of major accidents involving instrumentation equipment. Submit the accident analysis report for instrument equipment to the Motor Department in a timely manner. (IX) Establish and maintain records and archives for instrumentation equipment. (10) Formulate plans for the purchase, renewal, disposal, and maintenance of instrumentation equipment. Chapter 3: Preliminary Management of Instrumentation Equipment Article 8: The preliminary management of instrumentation equipment encompasses all the management tasks related to planning, design, selection, procurement, installation, completion, and commissioning during the entire process. It is an important aspect of comprehensive management; to ensure the lowest lifecycle costs and the highest overall efficiency, it is essential to pay attention to this preliminary management phase. Article 9: The planning of instrumentation equipment is primarily based on factors such as the enterprise’s production and business development direction, the requirements of the safety production and product quality assurance systems, and the trends in the development of instrumentation equipment. The department in charge of instrumentation is responsible for formulating the company’s instrumentation plan. Article 10: The department in charge of instrumentation equipment shall participate in the design review of instrumentation equipment for projects such as new construction, renovation, and expansion. It shall set requirements regarding the reliability, maintainability, suitability, cost-effectiveness, advancement, and safety of the selected designs, adhering to the principles of safety and reliability, technical advancement, and economic rationality. Article 11: The purchase of instrumentation equipment shall adhere to the principles of prioritizing quality, high performance-to-price ratio, and lowest life-cycle costs. Strict quality inspection upon arrival at the facility is required, and imported equipment must come equipped with the necessary spare parts for maintenance. Article 12: The units responsible for the installation of instrumentation equipment in new construction, renovation, and expansion projects must possess the appropriate construction qualifications, the capability to carry out work in accordance with design requirements, and a sound quality assurance system. The construction of instrumentation equipment must be carried out in accordance with the design requirements and the \"Technical Specifications for the Construction of Petrochemical Instrumentation Projects\" (SH 3521-1999). Article 13: The department in charge of instrumentation equipment shall participate in or be responsible for tasks such as the completion inspection, commissioning, and handover of completion documents for instrumentation equipment projects. At the time of handover, the completion acceptance must be carried out in accordance with the design requirements as well as the \"Code for Construction and Acceptance of Automation Instrumentation Projects\" (GB 50093-2002) and the \"Technical Specifications for Construction of Petrochemical Instrumentation Projects\" (SH 3521-1999), with the handover proceeding in accordance with the prescribed procedures. To ensure that all completion documents are available, the documents required for the project’s completion acceptance should include: (1) The as-built drawings of the project, which comprise the complete set of design drawings and as-built drawings for the instrumentation and automatic control systems ; (II) Documents for design modifications and substitute materials (III) Documents and records related to projects with potential hazards ; (VI) Ground resistance test record ; , (IV) Instrument installation and quality inspection records ; (V) Cable insulation test records ; (7) Records of cleaning, pressure testing, and leak testing for instrument air and pressure guiding pipes, etc. (8) Certificates of product quality compliance for instrument equipment and materials ; (IX) Instrument calibration and testing records ; (10) Records of loop tests and system tests ; (11) Instrument and equipment handover list ; (12) Records of alarm and interlock system debugging ; (13) Work orders for the configuration and recording of smart meters, DCS, SIS, and PLCs ; (14) List of unfinished projects, etc. Article 14: Before putting instrumentation equipment into use, the operation and maintenance unit shall formulate relevant procedures based on the characteristics of the equipment, and carry out technical training, accident response plan drills, and other related activities. Chapter 4 Classification of Instrumentation Equipment Article 15 Instrumentation equipment is classified into the following categories: (1) Process control systems ; (II) Testing instruments ; (III) Control instruments ; (IV) Interlock circuit instruments ; (5) Online analytical instruments ; (VI) Flammable gas and toxic gas detection alarms ; (7) Special instruments ; (8) Other instruments. Chapter 5 Management of Conventional Instruments Article 16 Conventional instruments refer to commonly used testing instruments, control and monitoring instruments, actuators, auxiliary units and their accessories, as well as laboratory analysis instruments, under normal circumstances. Article 17: The selection of conventional instruments shall follow the following principles: (1) While meeting production requirements, the selection of instruments should take into account their safety and reliability, technical advancement, and cost-effectiveness. (II) The instruments selected shall be qualified products that have been approved by the **technical supervision authorities and have obtained manufacturing licenses. Priority should be given to products that are certified under GB/T 19000 or ISO 9000 standards, or products that meet international standards. Untested prototype instruments that have not undergone industrial validation shall not be used in engineering design. (III) The selection of instruments should take into account the current situation and development plans of the enterprise, with an effort to standardize on mainstream models. (IV) The selection of instruments should facilitate centralized control and management across the entire plant or a specific area, as well as system integration, information integration, and functional integration, thereby improving the enterprise’s production management level. (5) For the routine instrument configuration and selection of newly built or renovated units, the provisions of the \"Code for Selection and Design of Automation Instruments in Petrochemical Industries\" (SH 3005-1999) shall be followed, and the departments in charge of instrument equipment in each enterprise should participate in or organize the review of the design documents. Article 18: The management of explosion-proof instruments shall meet the following requirements: Instruments used in hazardous areas must comply with the requirements regarding explosion-proof type and grade. Explosion-proof instruments shall have clear explosion-proof markings in prominent positions. When installing instruments in hazardous areas, the wiring must meet the technical requirements related to the explosion-proof type and grade. When maintaining explosion-proof instruments, it is not allowed to change the structure or material of the components. When upgrading or modifying existing explosion-proof instruments in hazardous areas, it is necessary to verify their explosion-proof performance, and the explosion-proof rating must not be reduced arbitrarily. When adding new instrument measurement and control circuits as well as other circuits in hazardous areas, their explosion-proof rating must not be lower than that of the other instruments in that area. Article 19: Radioactive instrument sites must have clear warning signs, and their installation and use shall comply with **standards. Article 20 Requirements for the use, daily maintenance, fault handling, and inspection of conventional instruments. (1) The inspection and maintenance department shall establish and improve various procedures and management systems for the operation, maintenance, calibration, and repair of regular instruments. (II) Personnel responsible for the operation and maintenance of instrumentation equipment must receive training and obtain the corresponding qualification certificates. (III) Maintenance personnel for special instruments must receive specialized training before they can carry out the maintenance and calibration of such instruments ; Radiological instruments should have dedicated maintenance personnel assigned to them, along with the necessary protective equipment and monitoring instruments. (IV) Strictly implement the regular inspection and mandatory maintenance systems for instrumentation equipment, and carry out planned maintenance work properly. The backup instruments should always be in good condition. (5) If any abnormalities or faults are detected while the instruments are in operation, maintenance personnel should address them promptly, and record the symptoms of the fault, its causes, the methods used for correction, and the results obtained. (VI) All standard instruments shall be subject to weekly inspections in accordance with relevant metrological regulations; the use of standard instruments that have passed their inspection deadline or failed inspection is strictly prohibited. (7) When maintaining and servicing the conventional instruments involved in interlocking, strict compliance with the requirements of Chapter 7 of this regulation shall be observed. (8) The maintenance of regular instruments is generally carried out during the shutdown for maintenance of the plant. Before starting the maintenance, a plan should be formulated based on the actual situation; necessary spare parts, maintenance materials, tools, and standard instruments must be prepared, along with a practical maintenance schedule. Maintenance projects that need to be outsourced must go through the outsourcing approval process. (IX) Instrument maintenance shall be carried out in accordance with the requirements of the \"Code for Maintenance and Repair of Petrochemical Equipment\" (SHS 07001–07008-2004) ; During each maintenance cycle, each instrument should be inspected and calibrated. (10) After individual calibration of the instruments, loop joint calibration should be carried out; for the instruments involved in interlocking, interlocking loop verification is also required. Article 21 Pressure Gauges: The calibration and maintenance of pressure gauges shall comply with the relevant regulations of the **metrology authorities. Before installation, the pressure gauge should be calibrated; a red line indicating the highest or lowest pressure should be marked on the dial. After calibration, the pressure gauge should be sealed with a lead seal. The pressure gauge should be selected according to the operating pressure. The maximum scale value on the pressure gauge dial should not be less than 1.5 times the operating pressure. Chapter 6 Control System Management Article 22 Control systems mainly include distributed control systems (DCS), safety instrumented systems (SIS), programmable logic controllers (PLC), industrial control computer systems (IPC), as well as host computers used in advanced process control (APC) and optimal process control (OPC) systems. Article 23: The Mechanical Department and the Instrumentation Team shall be involved in the overall management of all stages related to the design, installation, commissioning, and acceptance of the company’s control systems. Article 24: When planning and selecting control systems for new installations or renovations, or when developing, upgrading, or modifying existing control systems, the department in charge of instrumentation equipment shall review the design documents. The configuration and selection of control systems must not only meet the requirements for device production control but also feature a high level of technical advancement. Article 25: For control systems that are already in use, if the production process requires changes to the control scheme or the addition of instrument circuits, the facility concerned shall submit a request. The operations department will then handle the approval procedures with the production department, after which the mechanical department will be responsible for arranging for instrument technicians to carry out the necessary work, while keeping proper records of it all. Article 26 The management of control system rooms shall meet the following requirements: (1) A dedicated person must be assigned to manage the room. (II) The machine room environment must meet the requirements specified in the control system design. (III) Flammable, explosive, and toxic substances are strictly prohibited from being brought into the machine room; no miscellaneous items shall be piled up inside the machine room, and no objects shall be placed on the cabinets. (IV) Appropriate fire-fighting equipment should be available in the machine room. (5) The cable passages in the machine room should be equipped with rodent prevention measures to protect against rodents. Article 27: The management of spare parts for control systems shall meet the following requirements: (1) There shall be dedicated accounts and records for spare parts, so as to keep track of their inventory at all times; a sufficient quantity of spare parts should be maintained to ensure the stable operation of the control systems. (II) The environment in which the spare parts and components of the storage and control system are kept must meet the required storage conditions. (III) During the shutdown for maintenance of the equipment, power tests should be conducted on the spare parts to ensure they are in a ready state. Article 28: To prevent virus infections, it is strictly prohibited to use unrelated software on the control system, as well as to perform any operations that are not related to the configuration of the control system software. External hard drives, optical discs, and other media used for backups must not be used for other purposes, nor may they be used on other computers. Isolation measures should be implemented between the control system and the information management system to prevent external computer viruses from affecting the control system. The information management system is required to submit a report to the Operations Department, which in turn submits it to the company’s deputy chief engineer in charge of instrumentation for approval before work can proceed. Article 29: Daily maintenance, fault handling, and inspection management of control systems. (1) The integrity and operational status of the host and peripheral hardware should be checked regularly on a daily basis. Ensure that the environmental conditions meet the requirements for the proper operation of the control system ; The power supply and grounding systems meet the standards ; Perform equipment cleaning at the prescribed intervals. (II) System software and application software must have dual backups, which should be stored properly ; The password for the control system or the key to the keypad lock should be kept by a designated person, and operations must be carried out strictly within the specified scope ; Modifications to system software and major application software may only be carried out after approval by the competent authority and the company’s senior deputy chief engineer ; Software backups should include the software name, modification date, and person who made the changes, with relevant design modification documents archived. (III) If any abnormalities or failures occur during system operation, maintenance personnel should address them promptly, and record the symptoms of the failure, its causes, the methods used for resolution, and the outcomes. (IV) In principle, the inspection of the control system is carried out simultaneously with the plant’s shutdown for major repairs. During major repairs, a comprehensive and thorough cleaning of the system is required ; System debugging, diagnosis, maintenance, and calibration are to be carried out, as well as the verification of the interlock system ; During the major overhaul, the peripheral devices of the system also need to be inspected and tested. The maintenance of control systems shall be carried out in accordance with the requirements of the \"Code for Maintenance and Repair of Petrochemical Equipment\" (SHS 07008-2004). (5) Strengthen the management of control system failures, formulate emergency response plans for such failures, and continuously improve the ability to handle unexpected issues. (VI) Before carrying out maintenance operations on the system, technical preparations must be made to avoid blind operation. (7) Before maintenance, its attribute settings and the position of jumpers or switches must be checked and recorded ; The removed card components must be placed immediately in an anti-static plastic bag; they should not be left lying around casually. Article 30: The maintenance department must establish archives for system hardware and software, keep necessary records, and create an \"Operation Log\" and \"Maintenance Records.\" It is also required to develop a diagram of the network structure, as well as lists of hardware components and I/O allocation tables. Chapter 7 Management of Instrument Interlock Protection Systems Article 31 Interlocks are divided into process interlocks and equipment interlocks, and are classified into Category A and Category B based on their importance. Among them, the critical and important process system interlocks, as well as those that may lead to personal injury, equipment damage, or serious quality issues with the products, are classified as Class A interlocks. Article 32: The Operations Department shall classify the interlocks within the devices under its jurisdiction in accordance with the above definitions, compile them into a list of interlock classifications, and submit it to the Company’s Mechanical Affairs Department. After being reviewed by the Mobility Department in conjunction with the Production Department, it is submitted to the company office ; It shall be issued for implementation upon approval by the company’s deputy chief engineer in charge. Article 33: When it is necessary to modify interlocking systems (including changes to set values, interlocking procedures, principles, etc.), to discontinue or restore them, or to cancel such modifications, an application must be submitted in advance. The applicant shall prepare the approval form and submit it to the Mechanical Department or the Production Department for review. The Mechanical Department is responsible for equipment interlocks, while the Production Department is responsible for process interlocks. The reason, implementation plan, and preventive measures taken should be specified on the approval form. Article 34: The cancellation and restoration of interlocking shall be requested by the Operations Department or the Maintenance Department, while changes or cancellation of interlocking shall be requested by the Operations Department. Article 35: The cancellation of Class B interlocking shall be proposed by personnel at the level of technical assistant or above, approved with a signature by personnel at the level of chief engineer in charge of the system, and authorized by personnel at the level of deputy department head or above. The cancellation of the Class A interlock protection system is proposed by the chief engineer in charge of the equipment, approved with signatures from personnel at or above the deputy department head level, and authorized by the head of the company’s Production Department or Machinery Department. For the deactivation of important interlocks related to the safe operation of installations and large-scale equipment, the Mechanical Department shall submit a request for approval to the company’s deputy chief engineer, based on the actual circumstances. Article 36: Changes or cancellations to interlocking systems shall be proposed by the engineer in charge of the equipment, approved by personnel at the department head level or above, and submitted to the Mechanical Department for approval by the technical supervisor in charge at the company’s general management office before implementation. Article 37: The restoration of interlocking shall be proposed by personnel at the level of technical assistant or above, approved with a signature by personnel at the level of chief engineer in charge of the equipment, and authorized by personnel at the level of deputy chief engineer or above. Article 38: After approval is granted for making changes to, disabling, restoring, or canceling the interlocking protection system, it is necessary to obtain an interlocking work order from the Mechanical Department prior to carrying out the work. The order must specify in detail the basis for the work, the person responsible for carrying out the work and the supervisor, the contents of the work, and the time schedule for its completion. Article 39: To prevent misoperations, a two-person operation system must be adopted, with one person performing the operations and another providing on-site supervision. Before operation, the interlock status should be carefully checked and verified, and close communication should be maintained with the process operators during the operation. After the task is completed, the person who carried out the task and the supervisor must record the details of the task on the interlock work order and sign to confirm it. Article 40: The maximum period for lifting interlocking is 6 months. Interlocks that cannot be put into use after more than 6 months must have their approval forms processed again. Interlocks that are ready for operation should have the procedures for resuming use carried out promptly, so as to be put back into service as soon as possible. Article 41: Before starting up a new installation for trial operation, or before putting equipment back into service after maintenance, all interlock circuits must be thoroughly inspected and verified, and the interlock protection system must be calibrated. The interlock inspection test for the new equipment is led by the Engineering Department, which organizes the relevant units to complete it prior to the handover. Based on the test results, an interlock test form is filled out and signed by the personnel who conducted the inspection; this form is then submitted as part of the handover documents to the Machinery Department for storage. After the device is repaired, the interlock test is requested by the device technicians to the Mechanical Department, which then organizes professionals in mechanical, electrical, and instrumentation fields to carry out the test together with process engineers. The test results are recorded on a test form, and those who participated in the interlock test must sign on this form. Three copies of the interlock test form are prepared, with one copy kept by the Operations Department, one by the Maintenance Department, and one by the Operation Department. Article 42: Important interlock protection systems must be clearly marked. Article 43: When adding a new interlocking protection system, complete drawings and documentation must be provided. Article 44: The emergency stop buttons of the interlocking protection system shall be equipped with reliable guards. Article 45: The switches and buttons on the panel of the interlocking system are operated by the operators, while the switches and buttons behind the panel are operated by the instrument technicians. When instrument operators are working on the interlock system and need to operate switches, buttons, etc. on the control panel, they must first contact the process supervisor and obtain permission before proceeding with the operations. After the task is completed, the operator must be notified promptly so that they can check the status of the process and reset switches, buttons, etc. Article 46: The components used in the interlocking protection system (including primary sensing elements and actuating elements), as well as the computing units, shall be calibrated according to their respective specified calibration cycles. Typically, maintenance, inspection, and calibration can be carried out during major shutdowns of the equipment. Newly replaced components, instruments, and equipment must pass inspection and calibration before they can be installed in the system. Article 47: The maintenance and repair of instruments in the interlock protection system shall be carried out in accordance with the requirements of the \"Procedures for Maintenance and Repair of Petrochemical Equipment\" (SHS 07007-2004). Article 48: The interlocking protection system shall be equipped with sufficient spare parts, the types and quantities of which shall be stocked in accordance with the reserve standards and the regulations on spare parts management. Article 49: This system applies to all operational departments of the company; branch companies and subsidiaries shall follow it accordingly. This system shall come into effect as of the date of issuance. Article 50: The right to interpret these regulations lies with the Company’s Logistics Department. Chapter 8: Management of Flammable and Toxic Gas Detection and Alarm Devices. Article 51: For any newly constructed, expanded, or renovated production facilities as well as storage and transportation facilities where there is a possibility of accidental leakage of flammable or toxic gases, whether they are imported projects or domestic projects, flammable and toxic gas detection and alarm devices must be installed in accordance with the “three simultaneities” principle. Article 52: The installation and selection of combustible and toxic gas detection and alarm devices shall strictly comply with the provisions of the \"Design Code for Detection and Alarm of Combustible and Toxic Gases in Petrochemical Enterprises\" (SH 3063-1999). The selection of alarm devices shall comply with the following requirements: (1) The functions, structure, performance, and quality of combustible gas alarms shall meet **legal requirements**, and they must obtain a manufacturing license for measuring instruments issued by the **relevant metrology administration department**, as well as an explosion-proof certification issued by a **designated explosion-proof inspection agency**. (II) Advanced technology, stable quality, rapid response, easy maintenance, and guaranteed supply of spare parts. (III) Select the explosion-proof type of detector based on the classification of explosive hazard zones in the location of use ; Select the explosion-proof rating and group of the detector based on the category, level, and group of the flammable gases to be detected in the location of use. (IV) When the usage environment contains substances such as sulfur, arsenic, phosphorus, and halogen compounds that can poison the detection elements, an antidotal detector should be selected. (5) Multi-point indicator alarms shall have relatively independent alarm functions that do not affect each other, and be capable of distinguishing and identifying the location code of the area where an alarm is triggered. Article 53: The installation of combustible and toxic gas alarms must comply with the requirements specified in relevant standards. (1) Determine the installation height and location of the detectors based on the density of flammable and toxic gases as well as the prevailing wind direction. (II) The detector should be installed in a location free from impacts, vibrations, and strong electromagnetic field interference. (III) Minimize the impact of rainwater on the sensing elements as much as possible. (IV) When indicating alarms or their installation location, the principles of ease of operation and monitoring should be taken into account. The alarm should have a sign indicating the location of the corresponding detector, or a layout diagram of the detectors. (5) The installation and wiring of the detector shall be carried out in accordance with the requirements specified by the manufacturer, and shall comply with the relevant regulations for the installation and wiring of explosion-proof instruments. Article 54: Strengthen the daily maintenance, fault handling, and inspection management of combustible gas detection and alarm devices. (1) When the detector is of flameproof type, it shall not be used under conditions outside the specified range ; It is strictly prohibited to remove the detector while the instrument is powered on. (II) During daily routine inspections, the test button should be pressed to check whether the indication and alarm systems are functioning properly ; Regularly check whether the detector has been accidentally exposed to water, to prevent the detection elements from becoming wet and impaired in their performance. (III) The calibration of combustible gas and toxic gas detection alarms shall be carried out at least once a year, and it shall be arranged uniformly by the Motorization Department. Depending on the environmental conditions and the operating status of the instruments, the instrument team performs a ventilation task every three months to check and test whether the alarms are functioning properly, and records relevant information. Inspection and calibration personnel must hold valid metrology inspector certificates. Article 55: Combustible gas alarms shall undergo a comprehensive inspection once a year, and the maintenance and inspection shall be carried out in accordance with the requirements of the \"Code for Maintenance and Inspection of Petrochemical Equipment\" (SHS 07005-2004). Article 56: When calibrating combustible gas detectors, standard gases provided by units that have been approved and authorized by the metrological administration, possess the corresponding standard materials, and hold a \"License for Manufacturing Metrological Instruments\" should be used. Article 57: For the shutdown, removal, or addition of combustible gas alarms, the Operations Department shall submit an application; after approval by the Safety and Environment Department, the Maintenance Department will arrange the actual construction and related work. Chapter 9 Management of Online Analytical Instruments Article 58 The configuration and selection of online analytical instruments shall comply with the \"Specifications for the Selection and Design of Automation Instruments in Petrochemical Industries\" (SH 3005-1999); the department responsible for instrument equipment shall be involved in the selection and configuration of such instruments. The following principles should be considered when selecting online analytical instruments: (1) The selected online analytical instruments should be technologically mature, have reliable performance, and be easy to operate and maintain. (II) The analytical instrument technology selected shall meet the requirements regarding the operating temperature, pressure, and properties of the medium to be analyzed ; All the technical specifications of the instruments must meet the requirements of the process flow. (III) Online analytical instruments used for measuring corrosive media or installed in flammable and explosive hazardous areas shall comply with the provisions of relevant standards and specifications. (IV) The analytical instruments used in control systems must have linear ranges and response times that meet the requirements of those control systems. (5) When online analytical instruments need to communicate data with a DCS, there should be a universal communication interface, and its communication protocol and speed must be consistent with those of the DCS system. Article 59: Management of the use, daily maintenance, fault handling, and repair of online analytical instruments. (1) Personnel responsible for the operation and maintenance of online analytical instruments shall receive training and obtain the corresponding qualification certificates. (II) Strictly implement the regular inspection and calibration systems for on-line analytical instruments, and carry out planned maintenance work properly. The maintenance, repair, and calibration of online analytical instruments shall be carried out in accordance with the requirements of the \"Code for Maintenance and Repair of Petrochemical Equipment\" (SHS 07005-2004) as well as those specified in the respective instruction manuals for the online analytical instruments. (III) If abnormal readings or malfunctions are detected while the online analytical instrument is in operation, maintenance personnel should address them promptly, and record the symptoms of the malfunction, its causes, the methods used for correction, and the results obtained. (IV) All standard instruments shall be subject to weekly inspections in accordance with relevant metrological regulations; the use of standard instruments that have passed their inspection deadline or failed inspection is strictly prohibited. For calibration, standard gases provided by units that have been approved and authorized by the metrological administration and hold a \"License for Manufacturing Measuring Instruments\" along with the corresponding reference materials should be used. (5) When maintaining and servicing the online analysis instruments involved in interlocking, strict compliance with the requirements of Chapter 7 of this regulation is necessary. (VI) The maintenance and repair of explosion-proof online analytical instruments shall be carried out in strict accordance with the requirements of Article 18, Chapter 5 of these regulations. (7) The major overhauls of online analytical instruments are carried out along with the major overhauls of the installation ; During the major overhaul, a comprehensive and thorough cleaning of the on-line analysis instrument system is required, as well as system calibration, diagnosis, maintenance, and inter-system alignment. Online analysis instruments involved in interlocking should also undergo interlocking circuit verification. Article 60: Daily maintenance and repair management of sample pretreatment devices for online analytical instruments. (1) Strictly implement a regular inspection system for the sample preprocessing device; inspect it daily to ensure that parameters such as temperature, pressure, and flow rate of the samples to be analyzed meet the technical requirements of the online analysis instruments. (II) In the event of any abnormalities or failures during the operation of the sample preprocessing device, maintenance personnel shall address them promptly, and record the symptoms of the failure, its causes, the methods used for resolution, and the results obtained. (III) The maintenance and repair of the sample preprocessing device shall be carried out in accordance with the established procedures and the requirements specified in the device’s manual. (IV) When the plant is shut down for maintenance, the sample preprocessing units of the on-line analysis instruments should also be serviced, involving thorough cleaning as well as system calibration, diagnosis, and maintenance. Chapter 10: Management of Basic Information Article 61: The departments in charge of instrumentation equipment and various departments under the company shall, in accordance with their respective responsibilities for management, establish and improve registers, archives, and basic information related to such equipment. Article 62: The department in charge of instrumentation equipment shall establish, at a minimum, management systems specific to instrumentation, records of control systems such as DCS and PLC, records and statistical tables related to the interlock protection systems for critical equipment, records of flammable and toxic gas alarms, records of major defects, tables indicating the technical condition of automated instrumentation, and records of professional inspections. Article 63 The maintenance department shall establish and maintain at least the following records and ledgers: (1) Management systems specific to instrumentation, as well as maintenance procedures; (2) Ledgers for control systems such as DCS, SIS, and PLC, system acceptance records, records of system inspections and fault handling, and system modification records ; System design documents, manuals, system software, application software, system backup disks, etc. (III) Records of the instrument interlock protection system, interlock schematic/logic diagrams, statistical tables of the interlock system, etc. (IV) Records of flammable and toxic gas alarms, distribution maps of detection points, instrument manuals, circuit diagrams, calibration records, and other related documents. (5) All design documents and drawings for instruments, selection information, manuals, accompanying materials, auxiliary instruments and other equipment-related documents and drawings, as well as installation and commissioning records, acceptance records, maintenance and calibration records, etc. (VI) Table of the technical condition of automated instruments. (7) Records of instrument equipment failures and defects, instrument accident logs, etc. (8) List of automatic control equipment. (IX) Online analytical dashboard ledger. (10) Monthly inventory ledger for spare parts. Chapter 11: Management of Instrument Power and Gas Supplies Article 64: Management of instrument gas supplies: (1) The purified gas shall not contain flammable, explosive, toxic, harmful, or corrosive gases (or vapors). The dew point of the gas source at operating pressure should be at least 10°C lower than the local annual extreme minimum temperature in the working environment or historically. (II) The control room shall be equipped with monitoring and alarm systems for the pressure of the gas supply system. (III) Conduct a daily inspection of the gas supply system (air tanks, valves, pipelines, filters, pressure regulators, pressure gauges, etc.). (IV) Empty the in-use filters at least once a week (the frequency of emptying can be increased as appropriate depending on the quality of air supplied by the instrument and its installation location). Regularly empty the drain valve at the lowest point of the device. Article 65 Instrument Power Management: (1) Conduct regular inspections of all components of the power supply system, checking the operation of power supply cabinets, power distributors, various switches, fuses, and other components; any issues identified should be analyzed and addressed promptly. (II) For power supply boxes used in parallel, their operation should be checked online, ensuring that the output current of each power supply box does not exceed its rated value. (III) The markings on switches, power distributors, and power terminal blocks in the power supply system must be accurate and clear. Damaged or missing labels, as well as illegible handwriting, should be addressed promptly. (IV) All equipment in the power supply system shall have adequate measures to prevent small animals from entering arbitrarily. (5) The power supply switch for the instruments in the dashboard (cabinet) should have at least 10% of the circuit reserved as a backup. It is strictly prohibited to supply power to non-instrument loads from the instrument power supply ; It is strictly prohibited to connect temporary loads to the instrument power supply. (VI) Configuration principles for the power supply system of control instruments (VII) UPS units should be installed in the power supply systems for control instruments of critical production equipment, to ensure that such control instruments can display information properly and function reliably in the event of power outages or other disruptions in the power supply system of those production devices. (8) The wiring scheme of the power supply system for control instruments should be simple and clear. The power shall be derived from 380V/220V buses in different circuits (hereinafter referred to as low-voltage buses). The selected wires, equipment, protective devices, etc. shall comply with the relevant provisions of the Code for Design of Low-Voltage Distribution Systems GB 50054-1995. (IX) The configuration of the power supply system for control instruments allows for tasks such as offline maintenance of UPS units and regular maintenance of batteries, after ensuring the normal operation of the production facilities. (10) The switching device for the power supply system of control instruments shall enable a disturbance-free switchover, and its switching time shall meet the operational requirements of the control instruments ; Isolation transformers or voltage stabilizers can be installed in the direct feed circuits of low-voltage busbars, depending on factors such as the quality of the system power supply. (11) In the control instrument power supply system, lightning protection and EP harmonic absorption devices should be employed to prevent overvoltage from causing damage to this system. (12) Control instruments equipped with dual power supplies should be capable of operating simultaneously with two asynchronous power frequency AC sources. (13) The configuration of the power supply system for control instruments shall have the power requirements proposed by the instrumentation team, with the electrical and instrumentation teams working together to determine the appropriate configuration for this power supply system. (14) In the following situations, control instruments shall be configured with a two-power or three-power supply scheme. (1) Control instruments and important display instruments for large and medium-sized petrochemical production units and key utility systems. (2) Production equipment that operates under high temperature and pressure, and is flammable, explosive, toxic, or corrosive. (3) Production units with complex systems, featuring numerous process controls and interlocks. (4) Important online analytical instruments (such as those with process interlocks, etc.) ; (5) Monitoring systems for large-scale units and pumps, etc. Article 66 Technical management of the power supply system for control instruments. Quality indicators for ordinary power supplies: (1) Power supply voltage: 220V AC ±10%. Power supply frequency: 50HZ±1HZ. (2) The instantaneous power outage duration should be less than the allowable instantaneous power outage duration for the electrical equipment. Instantaneous voltage drop: less than 20%. Article 67 Operation Management: (1) After the completion of the control instrument power supply system, it may be put into use only after passing the joint acceptance by the electrical and instrument teams in accordance with relevant specifications. (II) Before starting up and feeding materials into the production unit at the beginning of each cycle, the reliability of the power supply system for the control instruments must be checked as follows: (1) Disconnect the output power circuit of the isolation transformer. (2) Disconnect the UPS output power circuit. (3) Disconnect the input power circuits for both the isolation transformer and the UPS at the same time. If the control instruments operate properly during the inspection and no abnormalities occur in the production equipment, the instrument power supply system is considered to be satisfactory. (4) The enterprise must draw a diagram of the primary power supply system for control instruments, and clarify the management boundaries between the electrical and instrumentation departments. (5) The operation and management of the UPS shall be carried out in accordance with the requirements of Sinopec’s \"Electrical Equipment and Operation Management System\" and relevant instructions. (6) In addition to complying with the management requirements for low-voltage distribution installations, the operation management of the power supply system distribution equipment for control instruments should also include the following tasks: (a) The distribution equipment should be equipped with a primary electrical wiring diagram. (b) The instrumentation and electrical departments must actively carry out operations, inspections, maintenance, and other tasks within their respective areas of responsibility, in order to eliminate any gaps in management. (c) Maintain records for the UPS and battery units, as well as records of operation, incidents, tests, etc. (d) The fault alarm signals of the UPS should be fed into the control instrument alarm system. (e) The neutral point at the output of the UPS power supply unit shall not be grounded. Article 68 UPS Management: (1) UPS is the abbreviation for “Uninterruptible Power System”. Its translated meaning is Uninterruptible Power Supply system, abbreviated as UPS. (II) For UPS power supplies used to supply important loads, a dual-unit power supply system is recommended; for particularly important loads, a dual-unit power supply system must be employed. (III) An online-type UPS should be selected (when the quality of the grid power meets the UPS output standards, its inverter operates in a hot standby mode), and its wiring should be simple and reliable. It operates in single-machine mode. It is powered by two independent power supplies. (IV) The UPS fault alarm signal shall be sent to the control room. (5) The UPS should be placed in a suitable operating environment; the optimal operating temperature is 25±5°C, and necessary dust prevention measures should be taken. (VI) Operators must undergo systematic theoretical and practical training before taking up their posts. (7) The technical personnel in charge of UPS should conduct regular operational analyses, and take preventive measures in a timely manner to address any existing issues and ensure safe operation. (8) UPS operation and maintenance personnel should possess professional knowledge of UPS equipment, ensure proper technical management of UPS operations, carry out all operations in accordance with regulations, conduct regular inspections, and record any abnormal conditions promptly to report them to their superiors or relevant authorities. (IX) Fully sealed valve-regulated or lead-acid batteries should be used, with a backup time of generally 15 minutes to 30 minutes. The maintenance department must conduct a verification capacity check on the UPS batteries once a year ; If it is not possible to inspect the operation of the production equipment, a plan should be formulated and implemented after obtaining approval from the supervising manager. (10) In the event of UPS equipment failures that pose a serious threat to safe operation, it is necessary to report them to the relevant authorities promptly and take effective measures to address them. (11) The instrumentation team shall establish integrity standards for UPS equipment and evaluate the equipment against these standards. (12) The instrumentation team shall maintain a UPS ledger detailing the date of installation, model, usage status, etc. (13) Rated capacity: When a single UPS is operating at full load, its load factor should be between 50% and 60%. (14) Basic technical specifications (1) Input power supply quality specifications: Input voltage: 3-phase 380V±15% or single-phase 220V±15%. Input frequency: 50HZ±2.5HZ. (2) Output power supply quality specifications: Output voltage: 220V±5%. Output frequency: 50HZ±0.5HZ. Output waveform distortion rate: less than 5%. (3) The instantaneous power-off time of the output power supply should be less than or equal to 20 mS. (4) The instantaneous voltage drop at the output is less than 10%. (5) Output harmonic distortion ratio: THD
4.1 Hierarchical Management of Measurement Equipment 4.1.1 Classification of Measurement Equipment Based on the technical characteristics, usage conditions, and importance of measurement equipment, as well as in accordance with relevant laws and regulations, and following the principles of risk-based management, focusing on key aspects while also taking general factors into account, implementing differentiated management, and ensuring comprehensive supervision, the measurement equipment within the company is classified into categories A, B, and C. All departments of the company shall, in accordance with the requirements of the \"Measurement Process Control Procedure\" document, identify the functions and measurement requirements at each measurement point in the measurement process; the Measurement Management System Office shall convert these into metrological requirements, and determine the control methods and levels of control. 4.1.1.1 Class A measuring equipment a. The company’s highest-level measurement standard used for value tracing and value transfer. ; b. Working standards for value transfer ; c. Reference materials used for the uniformization of measurement values ; d. Measurement equipment included in the list of devices subject to mandatory inspection, which is used for trade settlement, security protection, healthcare, environmental testing, and other purposes ; e. In process control during measurement, measuring equipment at key monitoring points where high accuracy of data is required, such as process control, quality inspection, energy metering, and business management. 4.1.1.2 Class B measuring equipment a. Measuring equipment used for the accounting of energy and materials within various secondary units of the company ; b. Measurement equipment installed at key monitoring points in the process control phase, such as process control, quality inspection, energy metering, and business management ; c. Measurement equipment used for cost accounting within company teams and workshops, as well as for awarding incentives based on production volume ; d. Measurement equipment used for precision testing ; Measurement equipment used to assist in production requires certain levels of accuracy and reliability in the data it provides. 4.1.1.3 Class C measuring equipment: a. Measuring equipment that is located in non-critical areas of the production process, is difficult to remove, and for which no strict accuracy requirements apply; such equipment serves only as an indicator or for reference purposes ; b. Low-cost consumable measuring equipment with stable measurement performance and readings that do not change easily ; c. Measurement equipment using tools for which no strict accuracy requirements apply. 4.2 Classification and management of measuring equipment 4.2.1 Class A measuring equipment a. The highest standard instruments, as well as those that are subject to mandatory inspection, must be managed in accordance with the \"Regulations on the Management of Working Measuring Instruments Subject to Mandatory Inspection in the People’s Republic of China\" issued by the State Council ; The Measurement Management System Office compiles a list of measurement devices that are subject to mandatory inspection, and submits it for **administrative registration with the metrology authorities. b. Standard materials used to unify measurement values must be carefully stored and used by designated personnel ; c. For measuring equipment classified as Category A, it is necessary to have a license mark indicating approval for the manufacture of measuring instruments as well as a factory certification at the time of purchase, and each unit must undergo inspection upon entry into stock. d. The number of Class A measuring devices available should ensure that these devices can be inspected on schedule, and that measurement activities can proceed normally during their calibration and repair periods. 4.2.2 Class B measuring equipment: a. When Class B measuring equipment arrives at the factory, it must be equipped with a license mark indicating approval for manufacturing measuring instruments as well as a certificate of conformity issued at the time of production; b. For measuring equipment that is installed on continuously operating devices and cannot be removed easily, its inspection and verification can be scheduled in conjunction with the maintenance cycle of those production devices ; c. Measurement equipment classified in Category B must be verified at specified time intervals, in strict accordance with verification procedures, calibration specifications, and the company’s own self-calibration standards. 4.2.3 Class C measuring equipment: a. For Class C measuring equipment, a one-time calibration (initial inspection) can be carried out to confirm its suitability, or the period of verification can be extended; however, during this verification period, regular supervision and inspection as well as comparison of readings should be intensified. If any failure in measurement performance is detected, the equipment should be replaced promptly ; b. For tool-type devices for which accuracy is not a strict requirement, as well as indicating measuring equipment, it is necessary to carry out regular maintenance and calibration during use; any defects should be repaired or replaced promptly, and re-verification must be conducted after repairs ;
Regulations on the \"Four Preventions\" in the Instrumentation Workshop during Winter
To carry out effective \"four prevention\" measures in winter and to fulfill the company’s requirement that no pipeline or valve should be damaged by freezing during winter operations, the workshop has formulated the following anti-freezing measures based on actual conditions: 1. Conduct regular inspections along predetermined routes (8:30–9:30 in the morning, 13:30–14:30 in the afternoon, 20:00–21:00 at night, and 1:00–2:00 in the early morning); increase the frequency of inspections in special circumstances. II. Inspection contents: 1. Electric heating: ① First, check whether the power switch for the heating system is closed and whether the power indicator light is functioning properly (verify this by checking the ammeter). ② Open the insulated box to check if everything is normal. ③ Inspect whether the insulation material is in good condition. 2. Steam heating: ① Check whether the valves on the insulated pipelines are functioning properly. ② Open the insulated box to check if everything is normal. ③ Check whether the drain devices are working correctly. ④ Inspect whether the insulation material is in good condition. III. Emergency measures: 1. Electric heating: ① If the power switch for the heating strip is damaged, it should be replaced immediately. ②When the heat tracing element itself is damaged, it should be replaced. ③When the heating strip is grounded, first locate the grounding point to eliminate the fault and restore power supply; otherwise, the heating strip should be replaced. 2. Steam tracing: First, check the tracing steam valve and clear the drain device; otherwise, replace the steam valve, pipelines, or drain device. 3. Once the instruments or pipelines freeze, locate them immediately and use steam or hot water to thaw them. Clear the drain devices or restore power supply to the insulation heating strips, and remove water or air from the system. Finally, restore the outer insulation layer to its proper condition. IV. Assessment Regulations: 1. Team members must conduct a thorough and detailed inspection of all instruments, pipelines, valves, etc. at the site on a daily basis, as scheduled (with a focus on anti-freezing measures, insulation, and waste removal). Those who fail to carry out these inspections on time will be fined 20 yuan for each instance. 2. If the duty personnel in each team notice that the insulation of the instruments is inadequate, they must address the issue promptly; if it cannot be resolved properly, shift handover is not allowed ; If issues are not addressed in a timely manner, resulting in freezing of instruments or pipelines, the person responsible will be fined 20 yuan. 3. Failing to conduct inspections without proper reason constitutes dereliction of duty, and the responsible person will be fined 100 yuan. 4. In the event that damage to instruments or pipelines occurs due to the aforementioned responsibilities, a penalty of 30% of the value of the damaged equipment will be imposed (with the technical personnel in charge and team leaders each bearing 5%, the person responsible bearing 10%, and the team bearing 10%) ; Responsibility is pursued in accordance with the accident management regulations underlying the incident. 5. The workshop duty personnel must check the status of the \"four preventive measures\" and the insulation conditions on a daily basis, and record these details in the duty log; otherwise, a fine of 20 yuan will be imposed on them for each incident. The duty personnel in each shift must strictly adhere to the shift handover procedures, and carefully record the status of instrument freezing prevention and insulation on a daily basis. Those who fail to fill in such records in a timely manner will be fined 20 yuan per incident. 6. Each team shall, based on the actual conditions of its own team, assign specific responsibilities for various instruments, equipment, related pipelines, valves, anti-freezing devices, etc.; these responsibilities must be clear and assigned to individual persons, with the relevant information posted on the wall. For those who have not implemented responsibility contracting, a fine of 200 yuan will be imposed on the team leader ; At the same time, the team leader shall bear all penalties resulting from unclear responsibilities. 7. During the winter \"four-prevention\" period, teams that manage to prevent their instruments, piping, valves, etc. from being damaged by freezing will receive a one-time reward of 600 yuan from the workshop ; A reward of 200 yuan was given to the respective technical staff and team leaders. 8. All teams are requested to carefully organize the study of the above provisions and ensure their implementation. Instrument Workshop
Instrument Management System: Measurement instruments are powerful tools that enable measurement personnel to exert control over engineering projects. Taking good care of measuring instruments and tools is a virtue that every measurement professional should possess. Since measurements are carried out outdoors and are affected by natural and climatic conditions, it is very important to take good care of the measuring instruments. Using them correctly and maintaining them properly are essential for ensuring the quality of measurement results, improving work efficiency, and extending the lifespan of the instruments; these are basic skills that every measurement technician must master. Otherwise, it will not only hinder the progress of the measurement work and the completion of tasks, but also cause damage to the instruments. To this end, we must use the instruments correctly, understand their performance, basic structure, and operating methods, and strengthen their maintenance. I. Configuration of instruments and equipment: Each project should, in light of the specific conditions of the project as well as the requirements of the owner and supervisor, equip itself with advanced surveying equipment wherever possible. This helps to increase the degree of automation in surveying work, reduce the workload on surveyors, improve work efficiency, and ensure the accuracy of the survey results. II. Allocation and acquisition of equipment: For current general projects, a large number of total stations are used; it is necessary to ensure that their selection is reasonable, appropriate, and cost-effective based on the actual conditions of the project. For new projects that require measuring instruments, the Engineering Management Department will allocate such instruments based on the company’s inventory of measuring equipment. If it is necessary to purchase new measuring instruments, a \"Instrument Purchase Request Form\" must be filled out, and the purchase can only take place after approval by the company’s senior management. For the transfer of project measurement instruments, the unit receiving the instruments and the unit transferring them must fill out an \"Instrument and Equipment Transfer Form\", indicating the condition of the instruments as well as any accompanying accessories. III. Use and Management of Instruments and Equipment (I) Unpacking, Packing, and Placement of Instruments 1. Before unpacking an instrument, the instrument box should be placed flat on the ground; it is strictly prohibited to unpack the instrument by holding it in the hands or carrying it, to prevent the instrument from being damaged if it falls to the ground during unpacking. After opening the box, make sure to check how the instrument is placed inside, so as not to put it back in the box in its original position after use. 2. Before removing the instrument from the box, loosen all the locking screws. When taking out the instrument, use one hand to support its base while holding the bracket with the other hand, and remove it gently; it is strictly prohibited to lift the instrument by the telescope or the horizontal axis. After removing the instruments and components used, the box lid should be closed promptly to prevent dust from entering the box. The instrument box is placed near the station; no one is allowed to sit on it. 3. When setting up the instruments, choose a location with a flat terrain and minimal construction interference, based on the position of the control points. Be sure to pay close attention to the instruments; check whether the instrument tripods are secure, and only release them after confirming that the screw connections are firm. However, it should be noted that the tightness of the connecting screw should be appropriate, neither too loose nor too tight. 4. After the observation is complete, the foot screw as well as the braking and fine-tuning screws should be returned to their normal positions, and dust on the upper surface of the instrument should be removed using lens cleaning paper or a soft brush. Then remove the instrument, hold it with both hands, and place it back in its original box in the same position as when it was taken out. Before closing the box, gently tighten each braking screw. Once it has been confirmed that all accessories are present, the box lid can be closed gently; it should be sealed properly before the lid is fully closed. Do not apply excessive force to avoid damaging the instrument. (II) Use and Management of Instruments 1. All types of measuring instruments shall comply with the regulations set forth by the Bureau Group Company regarding the management of measuring devices. 2. Newly purchased instruments and tools should be calibrated at a **legal metrological testing institution before use. For newly purchased instruments or those transferred to other projects, it is necessary to read the instruction manuals carefully. Starting from the basic operations and progressing to more advanced ones, one should practice repeatedly, summarize, and strive to become proficient in using the instruments so as to maximize their functionality. Those who are not familiar with the operation of these instruments should not use them blindly. 3. All types of measuring instruments must be regularly inspected and calibrated before and after use; proper maintenance should be carried out during use, and timely care should be given after use. 4. All types of optoelectronic and laser instruments must be regularly sent to qualified departments for inspection. The identification time should not exceed the specified time to ensure the accuracy and precision of the measurements. 5. It is strictly prohibited to use instruments that have not been tested and calibrated to their factory accuracy, that are past their calibration deadline, or those with defective parts or unclear readings. 6. When using a total station or a photometric rangefinder, it is prohibited to direct the telescope at the sun without a filter, in order to avoid damaging the eyes and the light-emitting diodes in the ranging unit. 7. When working in strong sunlight, during rain, or in humid conditions, it is essential to work under the protection of an umbrella. 8. Handle the instrument with care to avoid severe impacts and vibrations. Before setting it up, check the stability of the tripod. The staff must not leave the instrument throughout the operation to prevent accidents. 9. When changing stations, the instrument should be taken out of its case and packed, even if the distance is short. After the measurement work is completed, turn off the device, remove the battery, and pack it up. For long-distance transportation, appropriate shock absorption measures should be employed to prevent the instrument from suffering sudden vibrations. 10. Measurement instruments should be stored in a dedicated warehouse, with an environment that is dry, well-ventilated, and protected from shocks, fog, dust, and rust. The instrument should be kept dry; after being exposed to rain, it should be wiped dry and placed in a well-ventilated area to dry before being put back into its box. All instruments must not be exposed to pressure, freezing, moisture, or high temperatures; the instrument box should not be placed near stoves or heating pipes. 11. When transporting the instrument over long distances, proper measures must be taken to protect it from shocks and moisture. When loading, be sure to keep the instrument upright; it must not be inverted. When the measurer is traveling by car with the instruments, they should place the instruments on shock-absorbing pads or hold them on their legs to prevent damage from vibrations and bumps. 12. It is necessary to establish and improve systems such as registers for measuring instruments and equipment, cards for precision measuring instruments, and instrument archives. For the issuance, receipt, or relocation of instruments, registration and approval procedures must be followed. 13. Regarding the management of measuring instruments, the company’s precision measurement team formulates inspection and evaluation methods; units and individuals that excel in maintaining these instruments are rewarded. Those responsible for damaging the instruments due to improper use or poor storage shall be held accountable, and penalties shall be imposed as appropriate. 14. Measuring instruments and tools are considered unqualified if they are in the following conditions: damaged ; Overload or misoperation ; The functionality has shown suspicious behavior ; Display is abnormal ; The specified weekly inspection verification interval has been exceeded ; The integrity of the instrument seal has been compromised ; When optoelectronic and laser instruments have exceeded their service life, suffer from severe zero drift, produce unstable measurement results, and have low reliability of those results, it is necessary to apply for their disposal ; When conventional instruments cannot be repaired after damage, or when they are worn out, their readings are difficult to discern and their performance is unstable, affecting the quality of measurements, it is necessary to apply for their disposal. 15. Requests for the purchase of measuring instruments as well as their disposal are submitted by the project department to the company’s engineering management department, where they are approved by the company’s chief engineer and relevant supervisors. The company’s precision measurement team checks the instrument allocation and management across all projects every six months, ensuring that the records, actual items, and cards are in agreement and that all technical documentation is complete. 16. Measuring instruments must be kept under the responsibility of a designated person. For valuable and precise measuring instruments (such as total stations, precision levels, and laser plumb bobs), it is necessary to assign a specific person to take care of them, to use them only by that person, and to send them for inspection by that same person; others are not allowed to use them casually in order to prevent damage and loss of accuracy. (II) Incentives and Penalties for Instrument Management 1. In order to strengthen engineering survey management, promote scientific management of such activities within our company, prevent survey-related accidents, meet the needs of economic development, and fully leverage the enthusiasm and creativity of survey staff, necessary spiritual and material rewards will be given to those units and relevant leaders who excel in engineering survey management after a project is completed. Those who are diligent and thorough in their measurement work, study diligently, are proficient in their tasks, improve their skills, and achieve outstanding results can be recommended for promotion. 2. Those who, in their production and business activities, violate measurement and metrology regulations, engage in fraud, fail to enforce measurement and metrology management systems properly, and cause losses to projects due to errors in measurement work, should be subject to appropriate penalties. Those who conceal measurement accidents from reporting must be held accountable, along with the supervisors and relevant personnel. 3. Failure to manage measuring instruments properly and inadequate storage, which leads to damage and affects their normal use; the responsible persons will be punished depending on the severity of the situation. 4. The project’s engineering department shall establish appropriate management procedures for measuring instruments based on the actual conditions of this project, to ensure that such instruments are in good condition and accurate. In summary, in order to strengthen the management of measuring instruments, standardize the relevant management systems, ensure that these instruments are used correctly and with accuracy that meets the requirements of relevant standards, so as to obtain accurate and reliable measurement data that can better serve our engineering projects and guarantee effective control in engineering surveys, it is hoped that everyone will comply voluntarily.
Instrument and Meter Management System (I) Concept of Instrument and Meter Management 1. Definition of instruments and meters. Instruments and meters used in industrial enterprises refer to devices used for characterizing the surface condition, technical properties, and other characteristics of products, as well as for measuring, calculating, controlling, testing, and indicating the status of the production process; among these, those that are used solely for indication are called meters. In a broad sense, instruments are tools that enable humans to observe, detect, regulate, and control the physical movements of the objective world. 2. The tasks of instrument management at the team level in enterprises. The management of instruments and meters in work teams refers to the overall set of tasks involving the requisitioning of instruments and meters needed for production, their proper use, careful maintenance to maintain their performance and accuracy, as well as compliance with various management regulations. The tasks related to the management of instruments and meters in work teams are as follows: First, implement the systems for the management of instruments and meters ; Second, use instruments and meters properly to ensure their proper operation as well as the reliability and accuracy of the data obtained ; Third, carry out proper maintenance, storage, inspection, appraisal, disposal, accounting, record-keeping, and statistics ; Fourth, keep the technical documents (including certificates of conformity) properly ; Fifth, handle instrument and gauge accidents properly. (II) Specific tasks for the management of instruments and meters in enterprise work teams 1. Issuance of instruments and meters and establishment of records. The team formulates process plans for new products and renovation plans for equipment and instruments in accordance with the provisions of the production process documents, identifying items that are still incomplete or need to be added. Then, the workshop technician submits the request to the competent authority for approval or to obtain a plan for acquiring the instruments. Upon arrival, go through the pickup procedures, establish an account card, and inspect the instruments. The team’s inspection of instruments is usually carried out in conjunction with the instrument operator, and it includes an external inspection, that is, checking whether the outer packaging is damaged ; A comprehensive inspection involves checking the main unit, auxiliary equipment, accessories, special tools, accompanying drawings, technical documents, instructions, as well as peripheral device connections, all in accordance with the packing list and instructions ; Performance testing involves checking each item in accordance with the technical specifications specified in the manual. For large, precision, and rare instruments, an acceptance report must also be filled out, and the drawings and technical documents should be submitted to the higher-level authorities for archiving; the work team generally only keeps the instruction manual (or a copy of it). 2. Use instruments correctly. First, pay attention to the operating environment and conditions of the instruments. General instruments and meters have specified operating conditions, such as operating ambient temperature and humidity, which must be strictly followed. Check the certificate of conformity before use; instruments without such a certificate should not be put into operation. Under normal conditions, the area where the instrument is operated should be well-ventilated, free from strong magnetic fields, corrosive substances, and severe vibrations; attention should also be paid to dust prevention. Second, use instruments within the scale permitted by technical specifications. There is no universal instrument in the world; all instruments are designed to perform functions of observation, detection, adjustment, and control within a specific limited area. Therefore, they must be used within their designated scope. It is necessary to ensure that all instruments and equipment operate properly, without using inferior substitutes for high-quality ones, and without exceeding their capacity limits. Ordinary instruments are all adjusted and calibrated, and some of their components are sealed; it is not allowed to disassemble or take apart these instruments without permission. When in use, appropriate force should be applied to the operating and control handles, shapes, and buttons. Third, pay attention to the operating procedures for the instruments. Before use, check whether the power supply and other power sources are compatible, have proper contact and sealing, and whether all peripheral accessories are properly configured; only after everything is ready can the device be turned on. All radio instruments have a preheating and stabilization process, which should be taken into account when using them. Other operating sequences, methods, continuous usage time, accuracy of use, limits of use, etc., shall be carried out in accordance with the regulations. 3. Comply with the periodic inspection system. To ensure the accuracy, consistency, and reliability of the functions of instruments and meters, the team must, in accordance with the regulations set forth by the relevant supervisory authorities regarding periodic calibration, submit these instruments and meters for inspection and calibration on time and in sufficient quantities. They must also handle the transfer of measuring instruments properly, and keep proper records of the calibration cards or forms. 4. Ensure proper maintenance of instruments and equipment. The main aspects of maintenance for instruments and equipment include dust prevention, moisture protection, corrosion prevention, and anti-aging measures. Wipe the casing with a dry cloth daily, and cover it with a cloth when not in use. Some instruments also require protection from light, and the dust accumulated on these instruments should be removed regularly by qualified personnel. 5. Ensure proper management of precision instruments and equipment. Precision, valuable, and rare instruments and equipment require thorough attention in terms of usage, storage, maintenance, and inspection. For such equipment, a management and maintenance system of “four fixations” and “five no’s” must be strictly implemented. First, the “four fixations” refer to: fixing the location of use, fixing the personnel responsible for use, fixing the personnel in charge of maintenance, and fixing the specialized management system. Second, the “five no’s” refer to: never leaving the device unattended while it is running, not using precision instruments in a careless manner, not operating them when they are faulty, not violating the operating procedures, and not stacking other instruments or items on top of the device. 6. Carry out other management tasks. First, ensure proper management of instrument accessories. The loss of accessories is a common occurrence during the use of instruments, and such losses or damages often prevent precision and expensive instruments from being used further, severely impacting production or research activities. Therefore, management must be effectively strengthened. The management method involves creating accounts for the accessories along with the instruments, designating fixed storage locations, establishing a borrowing system, and specifying the procedures for handing over instruments and accessories when they are used by different people. Second, ensure proper storage of instrument technical documentation. The instrument manuals, operating procedures, and other technical documents kept by the team should be stored together with the team’s process documents; when there is a change in team leader, these documents must be sorted out and handed over. These materials can only be borrowed and cannot be kept privately. Third, the handling of lost instruments and meters. In the case of instruments kept by individuals, any loss, whether due to subjective or objective reasons, must be dealt with seriously, and the matter must be reported immediately to the relevant authorities. Depending on the circumstances, administrative sanctions along with financial compensation should be imposed. All units should establish a compensation system for lost instruments. Fourth, the handling of instrument accidents shall follow the methods for dealing with equipment accidents. Fifth, the scrapping and utilization of instruments and meters. If instruments and equipment cannot be repaired due to long years of use, poor performance, severe damage caused by accidents, etc., or have lost their value as a result of technological advancements, the team can submit an application for disposal to the relevant authorities through the workshop. After technical evaluation and approval by the relevant authorities, the responsible department fills out a scrap application form, submits it to management for approval, and the item is then officially scrapped. Instruments that have been scrapped are handled uniformly by the competent authorities.
Regulations on Incentives and Penalties for Instrument Management 1 Purpose: To standardize the use of instruments, clarify the management responsibilities of instrument management organizations at all levels within the company, enhance the management of instruments in the company, ensure that instruments are under control throughout their entire lifecycle and operate safely and efficiently, prevent abnormal failures, and extend their service life; these regulations on incentives and penalties for instrument management are therefore established. 2 Responsibilities 2.1 The Instrument and Electrical Department is the department in charge of the company’s automatic control instruments; it is responsible for formulating regulations for the management of these instruments as well as creating standardized management forms ; Conduct regular or irregular inspections of various units’ compliance with management systems or requirements, announce the assessment results, and hold those responsible accountable. 2.2 The using department is responsible for implementing the “Instrument Management Incentive and Punishment Regulations” ; Responsible for training and cooperating with the relevant departments in investigating the causes of faults and conducting analyses. 3 Management Requirements 3.0 For measuring instruments such as those used for mandatory testing, it is necessary to unconditionally implement the **policy and conduct measurements on time ; 3.1 When repairing instruments and meters, application procedures must be followed in accordance with established processes and regulations; sending instruments to the repair department without the approval of the Instrumentation and Electrical Department is an illegal act ; 3.2 For equipment, instruments, and meters that suffer natural damage as a result of normal use, apply for repairs following the established procedures ; 3.3 For instruments and meters that are damaged due to abnormal causes, the person responsible shall fill out the “Investigation and Analysis Form for Equipment/Instrument Failures”, and the management department shall handle the matter in accordance with relevant regulations ; 3.4 For equipment or instruments determined to be damaged due to human error, the Instrumentation and Electrical Department shall organize an investigation to hold those responsible; if the department using such equipment failed to provide training to its employees, that department shall bear primary responsibility. If the department using it has already provided training to the employees, the person using it shall be held accountable. 4 Regulations on Rewards and Punishments 4.1 Regulations on Rewards for Instrument Managers 4.1.1 Every year, the instrument management department submits an application to the company for a reward fund to be used specifically to reward the instrument managers in various branches and departments ; 4.1.2 For instrument managers in the using departments and branch offices, if they accomplish the target tasks outlined in points 4.1.3 to 4.1.8 throughout the year, they will receive a full score of 100 points and be entitled to a full reward amount ; 4.1.3 100% timely rate for the inspection of measuring instruments, equipment maintenance, and fault resolution throughout the year ; 4.1.4 No failures of equipment or instruments caused by improper operation ; 4.1.5 No safety incidents occur ; 4.1.6 No loss of equipment or instruments ; 4.1.7 Submit the monthly summary table of equipment and valuable instrument utilization rates on time ; 4.1.8 Complete the training for new employees on operating equipment and using valuable instruments in a timely manner. 4.2 Penalties for Equipment and Instrument Administrators 4.2.1 In the event of any violation listed in 4.2.2–4.2.8, 10 points will be deducted from the department’s equipment and instrument administrator’s score each time (deducted from their bonus) ; 4.2.2 Failure to arrange for the calibration of measuring instruments, testing equipment, and pressure vessels as planned, or delay in submitting them for calibration ; 4.2.3 General accidents resulting from improper operations ; 4.2.4 Equipment and instruments under the jurisdiction of the relevant department that are lost throughout the year, with a total value of 5,000 yuan or more ; 4.2.5 Use of measuring instruments, testing equipment, and pressure vessels whose calibration validity period has expired ; 4.2.6 Taking the instruments outside without approval or lending them to persons outside the company ; 4.2.7 Failure to submit the summary table of equipment and instrument utilization on time ; 4.2.8 No training has been provided for new employees on operating the equipment and using valuable instruments, or no records of such training are available. 4.2.9 If the score for that year becomes negative, a fine of 50 yuan will be imposed each time, to be deducted from the salary. 4.3 Regulations on Rewards for Users 4.3.1 The using department selects 1 to 2 outstanding operators of equipment and instruments each year and provides them with appropriate rewards; the selection criteria can refer to the standards in paragraphs 4.3.2 to 4.3.5: 4.3.2 No record of illegal operation of equipment, instruments, or other violations throughout the year ; 4.3.3 Able to operate main or various different types of equipment and instruments skillfully ; 4.3.4 Fill in operation records promptly and clearly over the long term ; 4.3.5 Regularly guide new employees on how to use the equipment instruments correctly. 4.4 Penalties for Users 4.4.1 In the event of any violation listed in 4.4.2–4.4.8, the management department shall impose a fine of 50 yuan on the user ; 4.4.2 Misuse of equipment or instruments ; 4.4.3 Lending equipment or instruments to persons outside the company without approval ; 4.4.4 Failure to turn off the power to equipment or instruments after work hours (except when work needs to continue) ; 4.4.5 Sending faulty instruments to a repair shop without submitting an application form ; 4.4.6 Bringing valuable instruments into a test chamber where high or low temperatures are applied for measurement (damage to the instruments will be compensated separately) ; 4.4.7 Failing to send the equipment or instruments for inspection in a timely manner within the valid period for use in inspections ; 4.4.8 In the case of instruments and equipment that are damaged or lost due to human error, the responsible party shall compensate the company for the resulting losses; the proportion of the compensation amount is specified in clause 4.4.9. The perpetrator must fully compensate for the losses caused by deliberate vandalism or theft and bear legal responsibility ; 4.4.9 For equipment or instruments whose depreciation period has not yet expired, the compensation amount is calculated using formula (1): Compensation amount = Original value of the equipment or instrument × 10% + Depreciated net value × 10%. (1) For equipment or instruments whose depreciation period has already expired, the compensation amount is calculated using formula (2): Compensation amount = Original value of the equipment or instrument × 10% × (1 – Used years × 3%). (2) 6.5 Inspection and evaluation by the using department 6.5.1 The Instrumentation Department conducts inspections of the management of instruments and meters in the workshops on a monthly basis, and publishes the results of these inspections in the monthly “Statistical Report on the Quality of Instrument Management Work”. Praise departments that perform well in a timely manner, and offer criticism to those with existing problems. Departments that fail to make adequate improvements will have their situation reported to the company’s senior management, and accountability will be pursued. 7 Supplementary Provisions 7.1 The interpretation of these management regulations lies with the Instrumentation and Electrical Department of the company. 7.2 These management measures shall come into effect as of the date of issuance. :) :lol :lol Last edited by zlky2005 on 2008-12-15 10:22 ]
Shift handover system: This system is established in accordance with the company’s principles regarding labor organization and discipline, in order to regulate the behavior of electrical and instrumentation personnel and to facilitate more effective maintenance of such equipment. 1. The shift supervisor on duty that day is responsible for coordinating the assignments of the electrical and instrumentation team members throughout the day; all members must unconditionally comply with these arrangements. If there are other tasks to be carried out, they must inform the shift supervisor on duty in advance. 2. During the morning roll call, employees must gather at the basketball court and line up to proceed to the production area for shift handover. Except for those on leave, on vacation, on scheduled rest days, or engaged in maintenance tasks, those who fail to show up will be considered late; those carrying out tasks must explain the situation to the attendance officer. 3. During the shift handover, the departing shift leader first informs about any equipment issues that occurred during the shift and how they were resolved, as well as information regarding tools, cleanliness, and unfinished tasks. Then, the incoming shift leader assigns personnel and outlines the tasks to be carried out. 4. Shift handovers must be carried out seriously and thoroughly, with strict adherence to the “six handovers” and “six non-acceptances”. “Six Reports”: Completion status of tasks (including monthly plans, weekly plans, and completion of calls related to the position) ; Status of outstanding issues ; Implementation status of process technical specifications ; Handover of area hygiene and preparation for the next production shift ; The quantity and condition of spare parts, tools, equipment, and other materials on hand ; Submit the superior’s resolution and report on the implementation status. “\"Six no-acceptances\": Do not accept if the above six aspects are not clearly explained ; Records that are incomplete, inaccurate, or insufficient will not be accepted ; No connection if the equipment is not properly maintained or accidents are not handled properly ; I will not take on issues whose handling has not been clearly transferred ; If the process parameters are not met due to human error, acceptance will be denied ; Power disconnection and restoration procedures must be completed properly before any such action can be carried out (these procedures are applicable to electricians). Those who violate the above-handover regulations will have 5 points deducted from their score per incident; in cases of serious violations or incidents such as equipment damage, fines or suspension of work/overtime will be imposed. 5. A sign-in system is in place for leaving work at noon and starting work in the afternoon: 1) During winter, the working hours are 11:45 and 13:20; sign-ins are collected at 12:05 and 13:30. No late sign-ins or sign-ins on behalf of others are allowed, and those who do not sign or have their signatures done will be treated as being early or late. 2) During the summer schedule, at 11:45 and 13:55, the attendance officer brings out the attendance sheets; they are collected again at 12:05 and 14:05. No supplementary signatures or proxy signatures are allowed, and those who do not sign or have their signatures done in their place are treated as being early or late. (The attendance clerk is responsible for bringing out and collecting the sign-in books at the designated times.) 6. Roll calls are held at 17:00 in winter and 17:20 in summer; except for those on leave, on permission, or engaged in maintenance tasks, anyone who fails to show up will be considered to have left early. Those carrying out tasks must explain the situation to the attendance clerk. 7. During the roll calls at the start and end of work, before and after class, the shift leader summarizes the work completed and the tasks accomplished on the previous day (the current day). 8. Late arrivals and early departures will be handled in accordance with the assessment system and the company’s relevant management regulations. If there are three instances of being late or leaving early in a row, or five such instances in total within a month, the matter will be referred to the HR department for handling. 9. Sign-in and roll-call take place in the control room; everyone must line up neatly. First, the shift supervisor on duty that day handles the relevant tasks, followed by the attendance officer conducting the roll-call, and then the start-of-shift and end-of-shift meetings are held. 10. The work attendance system must be strictly enforced, and the attendance clerks must carry out their duties diligently and rigorously. 11. This system shall come into effect as of today.
Instrument automation design management 1: In principle, the design of instrument automation projects that require significant investment and involve complex technical aspects during renovation and upgrading should be carried out by the design department; secondary units are not allowed to carry out such design work on their own. 2 For the instrument automation upgrade projects identified by the company, the relevant departments provide detailed technical specifications; after thorough evaluation and technical approval by the company’s Operations Department, design work is commissioned. .3 The designer shall carry out the design in accordance with the requirements of the design commission and **relevant design standards and specifications. Prior to the design, a \"Feasibility Analysis Report\" should be prepared as necessary; after comparing various technical and economic options, the option that is both technologically advanced and economically reasonable should be selected. A preliminary design is prepared for review, combined with a cost estimate for submission for approval; once it is reviewed and approved by the company’s logistics department, the construction drawings are designed. 4 After the construction drawing design is completed, it undergoes review and any necessary modifications are made; thereafter, the drawings are stored in the database and distributed. 5 Designers should have a forward-thinking approach to technology, possess extensive knowledge of technical information, and employ advanced instrumentation and automation techniques.