Communication configuration issues between DCS and PLC systems

2009-02-06View Original

Thread Content

I would like to consult the technical experts: Our company uses a DCS system (DeltaV-v8.4) equipped with a Profibus communication card (Profibus-DP). There is a field station there that utilizes a Siemens S7-200 PLC system to control two circulation water pumps, thereby regulating the flow rate and temperature of the circulating cooling water used in the process. The station is equipped with a CPU 226 and an EM277 Profibus-DP communication card; shielded twisted pair cables are used to connect the station (S7-200) to the DCS system. Since I know very little about communications, I would like to ask the following question. 1. How are the communication settings and communication software configured for the sub-station S7-200? 2. What information do the PLC control points need to provide for DeltaV system communication configuration, and how is the DeltaV communication software configured? 3. How can one get started with configuring communication software? Thank you all for your support! jsnjhu
Reply #22009-02-06
Does the PLC support Profibus communication?
Reply #32009-02-06
The S7-200 does not support Profibus-DP by itself, but Profibus-DP communication can be enabled by adding an EM277 card.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.