Hardware alarm issue in ICS Triplex T8100 Trusted system

2009-02-06View Original

Thread Content

This post was last edited by zlky2005 on 2013-1-6 at 12:35. Unit 1 in our factory uses the T8100 Trusted system from ICS Triplex. These past couple of days, one of the three HEALTHY lights on the AI card T8431 has turned red; it returns to normal after being reset, but this problem keeps recurring. Has anyone used this system? Please help analyze what could be causing this issue – it’s urgent! ! ! ! ! ! This post was last edited by wwxlxh2006 on 2009-2-6 11:30.]
Reply #22009-02-06
If the HEALTHY indicator light on the AI card is on in an abnormal state, it indicates a problem with the AI card itself; check whether there is a short circuit in the input circuit of the AI card, or whether alternating current is leaking into the card and causing damage to certain channels. 1. Check the power supply for the AI. 2. Check whether there are any abnormalities in the inputs of all AI channels. 3. Contact the system supplier
Reply #32013-01-06
Check the instructions, and take a look at the AI configuration as well
Reply #42013-01-06
It’s probably pointless to reply now; diagnostic software can easily determine where the problem lies! As for the ability to reset, it’s because diagnosis takes time; during that period, the fault light can be reset, but the fault isn’t eliminated, which is why the alarm appears again! It could be a channel failure, or it could be a card failure! If you have similar issues, feel free to contact me anytime!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.