Seeking help with Siemens ultrasonic level gauges

2009-02-06View Original

Thread Content

There are 2 Siemens ultrasonic level gauges; regardless of the output value, it shows full scale on the PLC. When checking the voltage, it’s 28V–30V. What’s going on? Is it necessary to add resistors? Thank you!
Reply #22009-02-06
The voltage should be normal. It is recommended to first disconnect the on-site level gauge and directly apply a 4-20MA signal to the PLC channel; if the reading remains at full scale, then there is an issue with the setup, such as whether the unit of measurement is correct.
Reply #32009-02-09
Issues with the PLC acquisition card or software configuration
Reply #42013-09-09
Is there interference from high-voltage electricity? It’s probably interference voltage; check whether it’s direct current or alternating current

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.