【Daily Question 20090209】What are the requirements for grounding the shielding layer of a shielded conductor? Why?

2009-02-09View Original

Thread Content

What are the requirements for grounding the shielding layer of shielded conductors? Why? Answer: The shielding layer should be grounded at one end and left ungrounded at the other; the grounding point can be located at the electronic device or at the sensing element, depending on the desired anti-interference effect. If both sides are grounded, the shielding layer forms a circuit with the ground, and common-mode interference signals can enter the electronic device through the distributed capacitance between the wires and the shielding layer, causing interference. However, if one end is grounded and only one side remains at the same potential, the shielding layer does not form a circuit with the ground, so no interference signals can enter the electronic device, thereby preventing the intrusion of common-mode interference voltages from the ground. This post was last edited by Mobei Yihai on 2009-2-9 20:19.]
Reply #22009-02-09
The shielding layer should be grounded at one end and left ungrounded at the other; the grounding point can be located at the electronic device or at the sensing element, depending on the desired anti-interference effect. If both sides are grounded, the shielding layer forms a circuit with the ground, and common-mode interference signals can enter the electronic device through the distributed capacitance between the wires and the shielding layer, causing interference. However, if one end is grounded and only one side remains at the same potential, the shielding layer does not form a circuit with the ground, so no interference signals can enter the electronic device, thereby preventing the intrusion of common-mode interference voltages from the ground. This post was last edited by Mobei Yihai on 2009-2-9 15:21.]
Reply #32009-02-09
The shielding layer should be grounded at one end and left ungrounded at the other; the grounding point can be located at the electronic device or at the sensing element, depending on the desired anti-interference effect. If both sides are grounded, the shielding layer forms a circuit with the ground, and common-mode interference signals can enter the electronic device through the distributed capacitance between the wires and the shielding layer, causing interference. However, if one end is grounded and only one side remains at the same potential, the shielding layer does not form a circuit with the ground, so no interference signals can enter the electronic device, thereby preventing the intrusion of common-mode interference voltages from the ground.
Reply #42009-02-09
The shielding layer should be grounded at one end and left ungrounded at the other; the grounding point can be located at the electronic device or at the sensing element, depending on the desired anti-interference effect. If both sides are grounded, the shielding layer forms a circuit with the ground, and common-mode interference signals can enter the electronic device through the distributed capacitance between the wires and the shielding layer, causing interference. However, if one end is grounded and only one side remains at the same potential, the shielding layer does not form a circuit with the ground, so no interference signals can enter the electronic device, thereby preventing the intrusion of common-mode interference voltages from the ground.
Reply #52009-02-09
The installation requirements for shielded cables specify that one end of the shielding layer should be grounded, while the other end should remain ungrounded. If both ends of the shield wire are grounded at the same time, common-mode interference signals can enter electronic devices through the distributed capacitance between the wires and the shield layer, introducing interference signals; in severe cases, this can prevent the electronic devices from functioning, posing a serious threat!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.