【Daily Question 20090214】 A calculation problem

2009-02-14View Original

Thread Content

Given: A flow measurement system consists of a 0.75 class standard nozzle, a 0.25 class differential pressure transmitter, a 1.0 class square rooter, and a 0.5 class display instrument. Find: 1. The accuracy class of this measurement system; 2. If the flow measurement range is 300–1250 T/h, determine the measurement error of this system. ryu=(0.752+0.252+1.02+0.52)1/2=1.369 δ= ryu%A=1.369%X(1250-300)=13.01T/h Last edited by liwei2002 on 2009-2-17 08:27]
Reply #22009-02-15
Solution: ryu = (0.752 + 0.252 + 1.02 + 0.52)1/2 = 1.369; δ = ryu/%A = 1.369% × X(1250 – 300) = 13.01 T/h
Reply #32009-02-15
Why does it always end in a 2? Why is the average accuracy multiplied by 1/2? Why not use the maximum range value to calculate the error? This post was last edited by chmyh on 2009-2-15 09:50]
Reply #42009-02-17
In the calculation formula, it’s not just a factor of 2 added at the end; rather, it’s the square of 2 and the square root of 1/2. Check my answer to the original question. The error is an error of the range, not an error of the maximum measurement limit; therefore, it is a difference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.