Can the inverter start this fan?

2009-02-15View Original

Thread Content

There is currently a 7.5KW fan that attempts to start using a 15KW generator, but it fails to start properly. The rated current of the generator is 28A. Now, a 7.5KW inverter is planned to be installed; could someone please advise whether this will enable the fan to start properly?
Reply #22009-02-16
The output current of an inverter during the startup phase is generally set at 1.25 times the rated current. The output current of a 7.5 KW inverter during startup is around 22 amps, which is less than the rated current of the generator; therefore, the motor can start when it is started under no-load conditions.
Reply #32009-02-17
It should be possible to start it; with a generator of this size, the theory of soft starting makes it entirely feasible to start the fan, so there’s no problem at all with using variable frequency drive. It’s a bit difficult to start it directly, haha.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.