There is a fault that occurred after a transmitter was installed

2009-02-17View Original

Thread Content

There is an existing transmitter; after it is installed, both the pressure and temperature readings displayed by the transmitter are abnormal, and this also affects the proper functioning of other instruments in the vicinity. The gauge pressure is normal. What could be the reasons for that?
Reply #22009-02-17
Remove it quickly; based on the symptoms you described, it is likely that there is a short circuit or ground fault inside this device, and continuing to use it could lead to serious accidents.
Reply #32009-02-17
Thank you to the person above; I’ve learned a trick too, thanks
Reply #42009-02-17
First, use HART to check whether it’s a setting issue before determining if there is a hardware fault.
Reply #52009-02-17
Check whether there are any interferences such as electric fields or radio waves at the site. Our company has encountered a situation where, during on-site calibration of instruments, communication using walkie-talkies affected the transmitters
Reply #62009-02-17
Check whether it is a power supply issue, or if the gauge itself is short-circuited, or if there is poor grounding in some areas
Reply #72009-02-21
It is estimated that there is a short circuit or ground fault inside this meter, causing a voltage drop of 24V, which in turn affects the proper functioning of the other meters in the vicinity.
Reply #82009-02-21
I don’t understand; if there is a short circuit, the meter will give an error alarm and will not be usable at all. Let alone lowering the voltage of other meters; if that were the case, there would be serious problems with the system design.
Reply #92009-02-22
The instruments are grounded, and the channels of the system cards are not isolated from each other; therefore, this affects the instruments in the same group
Reply #102009-02-22
If it also affects the adjacent instruments, then caution is needed. First, remove that instrument to see if the adjacent ones return to normal operation. If they do, it indicates a problem with the wiring of that particular instrument; if not, the issue might lie in the settings of those instruments.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.