HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Do valves need to be installed in front of all instruments?

2009-02-17View Original

Thread Content

Do valves need to be installed in front of all instruments? Why? How to design it? :handshake
Reply #22009-02-17
Valves are generally installed in front of instruments, mainly to protect the instrument chamber
Reply #32009-02-17
This thing is easy to replace; installing a valve makes it convenient to isolate it. If you think it won’t break, you don’t have to install it.
Reply #42009-02-17
The standard setup in front of the instrument panel includes 3 valves: the drain valve is used for pressure relief and maintenance purposes, the secondary valve is used to shut off the branch pipe, and the primary valve serves as a backup means of shutdown in case the secondary valve fails. Some valve assemblies come equipped with drain valves and secondary valves; thus, a valve assembly together with a primary valve constitutes the instrument piping system. The valves in these instrument pipes are primarily used for protecting the instruments and facilitating maintenance work on them
Reply #52009-02-17
There are many instruments that need to be calibrated regularly; if control valves are not used, production must be halted in order to carry out calibration or maintenance
Reply #62009-02-17
It’s best to have it installed, as it is convenient for maintenance, replacement, and calibration
Reply #72009-02-17
It usually has to be installed! There are also exceptions: temperature transmitters
Reply #82009-02-17
Most of them require valves, and the type of valve used also matters. However, there are exceptions; for instance, some temperature transmitters do not come equipped with valves, and sleeve-type measuring instruments such as those used for measuring the density and temperature of pulverized coal in pressurized gasification processes certainly do not need valves either
Reply #92009-02-17
Most instruments are equipped with valves, but devices that can be switched, such as pressure gauges at the pump outlet, may not need valves, as pumps usually have a primary and a backup unit, allowing for switching when replacing or repairing the instruments
Reply #102009-02-18
It is generally necessary in order to reduce the impact on the instruments and to facilitate maintenance
Reply #112009-02-18
It is necessary to install them in order to facilitate maintenance and protection of the instruments; some instruments also require the design of bypass circuits
Reply #122009-02-18
They are installed to protect the instruments. Generally, two valves are used: a primary valve and a secondary valve; the one that is closer to the instrument is called the secondary valve. These valves are collectively referred to as instrument valves
Reply #132009-02-18
It is generally necessary to install it for easy maintenance.
Reply #142009-02-19
Pressure instruments are necessary to protect the gauge from damage to its pointer when pressure increases suddenly. Thermometers usually come with a sleeve and do not require valves. There are two-valve assemblies, five-valve assemblies, etc
Reply #152009-02-19
Valves should be installed on the pipelines used for sampling, in order to enable isolation and discharge
Reply #162009-02-20
Valves are generally installed in front of the instrument; they serve primarily to cut off flow, making it easier to remove the instrument for repair and maintenance. The instrument may also have a vent valve. Since the valves on instruments are mainly used for cutting off flow, gate valves are typically employed
Reply #172009-02-20
It must be installed, after all, instruments are valuable items. It breaks easily. Valves are needed during maintenance. . . . :)
Reply #182009-02-20
Our pressure gauges and pressure transmitters are equipped with root valves, but there are no root valves at the flange roots of bimetallic thermometers, thermal resistance thermometers, thermocouple thermometers, or single-flange or double-flange differential pressure transmitters used for level measurement.
Reply #192009-02-20
Valves are generally installed in front of pressure gauges! It’s basically not necessary to add anything in front of the thermocouple! More practically, is it the pressure that’s a factor, along with temperature, fluids, etc.?~~~
Reply #202012-03-24
A valve bank plus a primary valve form an instrument loop; then is a three-valve bank itself considered an instrument loop in this case? Can another shut-off valve in the other three valve assemblies be used as a primary valve? Is this the correct way to understand it?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.