Causes of solenoid valve failure

2009-02-21View Original

Thread Content

After being in use for three to four months, the solenoid valves currently in use begin to show slow response, incomplete opening and closing, or fail to function. I would appreciate it if an expert could explain the reason. Thank you.
Reply #22009-02-21
I have encountered in practice: 1. Wear on the valve core and valve seat 2. The medium inside the valve contains impurities 3. There is a problem with the circuit; the operating voltage is low
Reply #32009-02-22
It’s also possible that 1: the sealing ring is allowing air leakage; in that case, it should be disassembled and lubricated, or the rubber ring should be replaced. 2. The coil plug is damp and corroded; open the junction box to address it. (Note: Make sure the sealing ring of the junction box is properly pressed in.) 3. Water or contaminants have entered the valve spool armature. (The exhaust vent should not face upward)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.