consult: What kind of oil can methanol be placed in a fire dike?

2009-02-24View Original

Thread Content

Can methanol and refined oil be placed in a fire dike? Can methanol and fuel oil be placed in a fire dike? Can methanol and paraxylene be placed in the same fire dike? According to what standards? If they cannot be put together, then they should be divided into two tank farms. Are there any spacing requirements between the two tank farms? This post was last edited by mountain16 on 2009-2-24 14:54 ]
Reply #22009-02-24
The methanol storage tank must be designed to be in a separate fire dike and cannot be mixed with oil or fuel. According to our factory's design, the spacing is 50M.
Reply #32009-02-25
"Petrochemical Enterprise Design Fire Protection Code" Chapter 5, Article 5.2.4, Article 5.2.5, and Article 5.2.7 all have clear requirements. Article 5.2.4 Storage tanks should be arranged in groups and comply with the following requirements: 1. In the same tank group, storage tanks with the same or similar fire hazard categories should be arranged. 2. Storage tanks for boiling and overflowing liquids should not be arranged in the same group as storage tanks for non-boiling and overflowing liquids. Storage tanks for liquefied hydrocarbons should not be arranged in the same group as flammable liquid storage tanks. Article 5.2.5 The total volume of the tank group shall comply with the following requirements: 1. The total volume of the fixed roof tank group should not be greater than 120000m3 ; 2. The total volume of the floating roof and internal floating roof tank groups should not exceed 600,000m3. Article 5.2.7 The fire separation distance between adjacent flammable liquid above-ground storage tanks in the tank group shall not be less than the following table: Liquid category fixed roof tank, floating roof tank, internal floating roof tank, horizontal tank less than or equal to 1000m3 and larger than 1000m3 Category A, B, B 0.6D (fixed fire cooling) 0.6D 0.4D 0.8m 0.75D (mobile fire cooling) Category C A 0.4D, but should not be larger than 15m ---- 0.8m Category C B 2m 5m ---- 0.8m This post was last edited by dreaming on 2009-2-25 16:33 ]
Reply #42009-03-10
"Petrochemical Enterprise Design Fire Protection Code" has now been published in the 2008 edition (GB50160-2008), and a lot of content has been updated. Where can I find it?
Reply #52012-04-10
Methanol can be placed in the same fireproof container as the oils you mentioned. For specific layout and isolation settings, please refer to the "Design Fire Protection Code for Petrochemical Enterprises" and "Design Code for Petroleum Depots"

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.