How to install the feed pipe on the top of the formaldehyde storage tank?

2009-02-24View Original

Thread Content

Dear friends, if the feed pipe of the formaldehyde solution is installed from the top of the tank, does it need to extend 20CM from the bottom of the tank? What's the basis? Thanks!
Reply #22009-02-25
Article 4.6.10 of the "Code for Fire Protection Design of Petrochemical Enterprises" states that when air may exist in a flammable liquid container, the inlet pipe should be connected from the lower part of the container.; If it must be accessed from the top, it should be extended to 200mm from the bottom of the container.
Reply #32009-04-16
7.2.14 When air may exist in the flammable liquid container, the inlet pipe should be connected from the lower part of the container.; If it must be accessed from the top, it should be extended to 200mm from the bottom of the container. When reviewing the drawings of the design institute, I also encountered such a problem. As said above. But I don’t know exactly why? Only fireproof and explosion-proof? If it is not a flammable liquid, can it be ignored?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.