【Daily Question 20090226】Instrument True or False Questions

2009-02-26View Original

Thread Content

1. To measure flow rate using an orifice plate, it should be installed in front of the control valve. Answer: Correct. 2. Regarding the range of a differential pressure transmitter, it can be adjusted arbitrarily as long as it is less than the standard range value of the instrument. Answer: Incorrect. 3. When checking back-blow type measuring instruments, instead of closing the check valve, the dirt is discharged from the instrument through the vent. Answer: Incorrect. 4. The gauge pressure measured using a U-tube manometer is related to the cross-sectional area of the glass tube. Answer: Incorrect. 5. When using a differential pressure transmitter to measure flow rate, the differential pressure is proportional to the square of the flow rate ( ). Answer: Incorrect
Reply #22009-02-26
1 pair, 2, 3, 4, 5 are wrong
Reply #32009-02-26
To measure flow rate using an orifice plate, it should be installed in front of the control valve. (Correct) 2. For the range of a differential pressure transmitter, it can be adjusted arbitrarily as long as it is less than the standard range value of the instrument. (Mistake) 3. When checking back-blow type measuring instruments, the primary valve is not closed; instead, dirt is discharged from the instrument through the vent. (Mistake) 4. The gauge pressure value measured using a U-tube manometer is related to the cross-sectional area of the glass tube. (Mistake) 5. When using a differential pressure transmitter to measure flow rate, the differential pressure is proportional to the square of the flow rate (Mistake)
Reply #42009-02-26
1. Right 2. Wrong 3. Wrong 4. Wrong 5. Wrong
Reply #52009-02-26
1 right, 2 wrong, 3 wrong, 4 wrong, 5 wrong
Reply #62009-02-26
1.R 2.W 3.W 4.W 5.W
Reply #72009-02-26
Answer: 1. √ 2. × 3. × 4. × 5. ×
Reply #82009-02-26
1 right, 2 wrong, 3 wrong, 4 wrong, 5 wrong
Reply #92009-02-26
1. √ 2 . × 3. × 4. × 5. ×
Reply #102009-02-26
1. True 2. False 3. False 4. False 5. False
Reply #112009-02-26
Answer: 1, True; 2, False; 3, False; 4, False; 5, False
Reply #122009-02-26
1. True 2. False 3. False 4. False 5. False
Reply #132009-02-26
Why do I think 5 is the right answer? Could someone explain this to me?
Reply #142009-02-26
Answer: 1. √ 2. × 3. × 4. × 5. ×
Reply #152009-02-26
5 is wrong; it depends on whether the activation is done at the transmitter or at the DCS, PLC, or secondary display instruments! ! ! 1 pair; 2345 is incorrect. For the second question, I think any value within the range of the transmission can be used as a new range point after verification, and that’s exactly what we do in practice. I wonder if everyone understands this question? This post was last edited by xu*ang309 on 2009-3-1 23:13]
Reply #162009-02-26
1 right, 2 wrong, 3 wrong, 4 wrong, 5 wrong
Reply #172009-02-26
1. To measure flow rate using an orifice plate, it should be installed in front of the control valve. (Yes) 2. As for the range of the differential pressure transmitter, it can be adjusted arbitrarily as long as it is less than the standard range value of the instrument. (Incorrect) 3. When checking back-blow type measuring instruments, the primary valve is not closed; instead, dirt is discharged from the instrument through the vent. (Incorrect) 4. The gauge pressure measured using a U-tube manometer is related to the cross-sectional area of the glass tube. (Incorrect) 5. When using a differential pressure transmitter to measure flow rate, the differential pressure is proportional to the square of the flow rate. (Incorrect)
Reply #182009-02-26
Answer: 1. √ 2. × 3. × 4. × 5. ×
Reply #192009-02-26
1 pair, 2, 3, 4, 5 are wrong

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.