The gas flow has stopped, so why does the flow meter still show a high reading?

2009-02-26View Original

Thread Content

The gas flow has stopped, so why does the flow meter still show a high reading? Is there some kind of interference?
Reply #22009-02-26
This is a systemic issue that requires an inspection of the entire circuit to determine the cause. First, it is necessary to ensure that nothing is flowing through the instrument’s measurement points, and then check whether there are any voltage stabilization mechanisms or other factors that might affect the readings
Reply #32009-02-26
There may be the following situations: 1. It is related to the type of flow meter; it is necessary to determine whether it is a volume flow meter or a mass flow meter. Generally, gas mass flow meters are greatly affected by water vapor. 2. It is related to the medium flowing within the pipeline; it is necessary to determine whether there is flow of medium in the pipeline, whether in the forward or reverse direction. 3. It is related to interference; it is necessary to check whether the flow meter has large vibration sources such as motors, as well as electromagnetic interference. Generally, minor disturbances can be eliminated through small-signal rejection
Reply #42009-02-26
First, check what type of flow meter you are using. Then verify whether there is indeed no flow of fluid in the pipe. Next, check if the zero point of the flow meter has shifted, and reset it if necessary
Reply #52009-02-26
The questions should be specific and detailed, such as the type of flow meter and the medium being measured; it can’t be about differential pressure, right? :lol
Reply #62009-02-26
1. First, check whether the manual valves before and after the flow meter are fully closed; if they are fully closed, the flow reading should be “0”. Of course, if a value is displayed at this time, it indicates leakage inside the valves used for isolation. 2. If no such leakage is detected, then check whether the zero point of the flow meter has shifted, and reset the zero point accordingly. 3. Verify whether there is any backflow of gas at the outlet end
Reply #72009-02-26
It should be interference caused by pressure and temperature
Reply #82009-03-01
From 2280 to 3100 – it changes within that range; it changes after some time passes. It seems like one of the modules is damaged; it was replaced today, and it seems to be fixed now
Reply #92009-03-07
It is a zero drift issue related to the instrument’s measuring elements; the zero point of the instrument needs to be set again

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.