Thread Content
Leak in the water wall, bed temperature 1, bed pressure drops; maintaining normal output from the slag cooler will not ensure a proper bed pressure. 2. The flue gas temperature drops behind the leakage point; if the leakage point is located in the furnace, the temperature at the thermocouple sensor located next to the leakage point is significantly lower than the temperatures at other sensors. 3. The deviation between the total amount of feedwater and cooling water and the steam generation volume increases. 4. The furnace pressure rises, and the output of the exhaust fan damper increases. How to activate the backup furnace? Which expert can help with the furnace startup steps?
In accordance with the operating procedures, 1. Inspect the standby boiler; 2. After confirming that the boiler is ready for operation, ignite it ; 3. Carry out all timing tasks properly during the voltage boosting process ; 4. Properly warm up the pipes between the standby boiler and the main steam pipe, as well as remove water from them ; 5. Merge furnaces. The method of merging furnaces is: ① Reduce the combustion in the standby furnace. ②For piping systems equipped with steam traps and bypass valves, the steam trap and bypass valve on the steam branch pipe should be opened in advance. ③When the boiler’s steam pressure is 0.5 MPa lower than the pressure in the steam header (0.05 MPa lower for industrial boilers), slowly open the boiler’s main steam valve. Immediately close the drain valve when there is no water hammer sound in the main steam branch, and only steam is discharged with no condensate ; Then open the main steam valve fully to supply steam to the generator (user) through the header. ④Close the bypass valve.