What is the starting method for a 22kw motor?

2009-02-28View Original

Thread Content

There is a 22KW motor used for mixing; what is a better starting method – star-delta or direct start? I’m not sure if this counts as overload – can the star-delta starter be activated? Thank you
Reply #22009-03-01
Star-delta starting is possible; first, check what capacity your transformer has. Generally speaking, 22 KW corresponds to a small motor, and direct starting is no problem as it reduces the number of potential failure points. Although the mixer is also considered a heavy-duty device, its gearbox provides significant speed reduction, so the torque reaching the motor side isn’t that high.
Reply #32009-03-01
Look at the transformer capacity; it should generally not exceed 20% of the transformer’s capacity. A 22KW unit should be able to start directly.
Reply #42009-03-01
Where are the transformers? Which is faster, a star or a triangle? Isn’t the starting current independent of the load?
Reply #52009-03-02
22. . . Can it be started directly?
Reply #62009-03-02
Is there a version without an inverter for driving the mixer? ? 22kw isn’t considered high either; it should be able to start directly
Reply #72009-03-02
It mainly depends on the capacity of your transformer; if it exceeds 20% of the transformer’s capacity, a reduced-voltage starting method should be used. If the transformer has a large capacity, direct starting is sufficient. Star-delta starting is used for light-load startups; if the startup load on the mixer is high, consider other voltage-reduction starting methods.
Reply #82009-03-02
A 22KW motor is not considered to be under heavy load; the key issue is whether the motor needs to start under load. If so, it is recommended to use a star-delta starting method.
Reply #92009-03-02
1. If there is a reduction gearbox on the load side of your motor, you can start the motor directly. 2. If there is no reduction gearbox, it is advisable to use star-delta starting, frequency-sensitive reactor-based voltage reduction starting, soft starter starting, or inverter starting.
Reply #102009-03-03
If starting under load, it’s necessary to do some calculations first. We all know that during star-delta starting, the torque at the beginning is only one-third of the normal value; the key question is whether this one-third torque is sufficient to drive the load Since yours is a mixer, you can calculate based on the operating principle of the mixing equipment and then decide how to start it.
Reply #112009-04-08
Small motor – just supply power directly! ! ! Generally, motors of this size are part of a motor group, and auxiliary starting devices such as soft starters are used for them.
Reply #122009-04-09
It can be started directly; however, when it is located far away from the transformer, the startup time takes a bit longer.
Reply #132009-04-09
Straighten up such a small motor.
Reply #142009-04-09
In our factory, 320KW units start up directly.
Reply #152009-04-09
The person upstairs can’t be from the same department as me, right? I have seen 300kw models with direct start, and I have also designed 280kw models with direct start. All the transformers are 1250… there are 2 of them: lol 22kw is considered a small motor. In the vast majority of cases, it can be started directly. Adhering to the principle of keeping it at no more than 30% of the transformer’s capacity ensures that the voltage drop remains within 15–20%. This is how I understand the blender the original poster is talking about. These days, many precision manufacturing processes emphasize speed control; you can ask if your process has any requirements regarding speed control. If available, use direct frequency conversion. The data is sent directly to the backend, which serves multiple purposes; P can reduce the impact wear that occurs during device startup.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.