SCR short-circuit fault

2009-03-03View Original

Thread Content

The soft starter (ABB) has experienced SCR short-circuit failures on several occasions; each time, the issue was resolved only by manual reset. Help is requested! ---The equipment is: Ingersoll Rand air compressor 110KW
Reply #22009-03-03
Check the soft start under no-load conditions, or use a dummy load for testing; then check whether the high starting torque of the air compressor is causing an elevated starting current :)
Reply #32009-03-03
Appropriate adjustments were made during that period, such as extending the start-up time for soft starting, but no improvement was observed. It was also observed that under no-load and loaded conditions, there was no significant difference compared to other air compressor units.
Reply #42009-03-05
It’s likely a quality issue with the soft starter; it is recommended to send it for repair. An SCR short-circuit fault is usually caused by an inability to shut it down effectively; this may be due to poor quality of the SCR itself or problems with the control circuit. Check whether the contacts of the plug-in are in good condition; if there are no issues, take it for repair.
Reply #52011-02-11
It seems to be related to automatic control, rather than issues in chemical engineering or environmental protection processes
Reply #62011-02-12
It’s probably a problem with the SCR device; replace it!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.