Converter ignition temperature
Thread Content
Please share the ignition temperature of your conversion furnace. For example: inlet temperature: 630–660, peak temperature: 610–630, outlet temperature: 550–570, water-to-gas ratio: 1.0. This post was last edited by wwg on 2009-3-4 at 20:55I. Temperature
TIC0401: Temperature of refined desulfurized coke oven gas – 200~380°C
TI0402: Temperature of raw coke oven gas – 250~380°C
TIC0403: Outlet temperature of superheated steam – 450°C
TIC0404: Temperature of steam-coke mixture – 650°C
TICA0405: Temperature of the water jacket in the oxygen conversion furnace – 90°C, 100°C
TRA0406: Upper temperature in the oxygen conversion furnace – <1450°C, 1450°C
TRSA0407: Temperature in the protection section of the oxygen conversion furnace – <1300°C, 1300°C
TRA0408: Catalyst temperature in the oxygen conversion furnace – ~1200°C, 1250°C
TRCA0410: Outlet temperature of the oxygen conversion furnace – 980°C, 1000°C
TIA0419: Water outlet temperature from the cooling water heat exchanger – 85°C, 95°C
TI0420: Oxygen temperature – 25°C
II. Pressure
PIC0401A: Pressure in the fuel gas main pipe – 0.3 MPa
PIC0401B: Pressure in the vent gas main pipe – 0.3 MPa
PI0402: Pressure of coke oven gas – 2.1 MPa
PICA0403: Oxygen pressure – 2.42 MPa, 2.65 MPa
PICA0404: Pressure in the medium-pressure steam main pipe – 3.9 MPa
PI0405: Pressure of steam-oxygen mixture – ~2.2 MPa
PI0406: Pressure of steam-coke mixture – ~2.0 MPa
PI0409AB: Pressure in the waste boiler drum of the conversion gas – 3.9 MPa, 4.1 MPa
PIC0410AB: Pressure of conversion gas – 1.7 MPa
PIA0415: Pressure of make-up cooling water – 5.4 MPa
PI0417: Pressure in the flue gas drum – 3.9 MPa
PI0418: Fuel pressure for the heating furnace – 0.2 MPa, 0.05 MPa
III. Level
LICA0401: Level of the vapor-water separation tank – 25%, 50%
LICA0402AB: Level in the flue gas drum – 50%, 75%, 25%
LICA0403AB: Level in the conversion gas drum – 50%, 75%, 25%
LICA0404: Level of the gas-liquid separator – 25%, 50%, 5%
LICA0405: Level in the stripping tower – 50%, 75%, 25%
LICA0406: Level in the cooling water buffer tank – 50%, 80%, 25%
IV. Flow Rate
FRC0401: Flow rate of coke oven gas – 19,767 Nm3/h
FRC0402: Flow rate of oxygen – 5,021 Nm3/h
FRC0403: Flow rate of process steam – 16,415 Kg/h
FRC0404: Flow rate of steam in oxygen – 2,461 Kg/h
FRC0405: Flow rate of steam for protective burners – 3,000 Kg/h
FR0406: Flow rate of fuel for the coke oven gas heating furnace – 1,562 Nm3/h
FR0407: Flow rate of fuel for the superheated steam heating chamber of the integrated heating furnace – 1,365 Nm3/h
FR0408: Flow rate of fuel for the steam-coke preheating chamber and steam-coke heating chamber of the integrated heating furnace – 1,207 Nm3/h
FRC0409: Flow rate of superheated steam – 15,638 Kg/h
FRC0410: Steam demand in the stripping tower – 8,000 Kg/h
FRQ0411: Steam generated by the flue gas waste boiler – 3,532 Kg/h
FRQ0412: Steam generated by the conversion gas waste boiler – 26,533 Kg/h
FRQ0413: Flow rate of demineralized water – 40,287 Kg/h
FRSA0415: Flow rate of coolant water for burners – 20 m3/h