2009-03-13View Original

Thread Content

Hello everyone, I am currently designing a chemical unit. The specification used is the "Building Regulations", but when arranging the liquefied hydrocarbon tank area, the construction regulations only say that there is no spacing requirement between the pump and the tank, but this time we are placing it outside the tank area. The construction regulations do not specify the spacing requirements outside the tank area. What should we do? Do we refer to the "Petrochemical Regulations" (Code for Design of Fire Protection for Petrochemical Enterprises). In addition, does the tank area refer to the space within the fire dike or an area? Thanks
Reply #22009-03-13
It may be unsafe to install a pump in a liquefied hydrocarbon tank farm unless your explosion protection is done well.
Reply #32009-03-13
Refer to the "Petrochemical Regulations" and it is best to call the local fire department for information.
Reply #42009-03-13
Reference to petrochemical design fire protection codes
Reply #52009-03-13
It is feasible to place liquid hydrocarbon pumps in the tank area, as long as electrical explosion-proofing is carried out as required, and the distance between the pump rooms when placed outside the tank area is calculated. It is recommended to refer to the urban gas design specifications.
Reply #62009-03-13
There are provisions in the building regulations, Article 4.2.7. The question you asked is explained in the table and its notes in this article. Please read it carefully.
Reply #72009-03-13
The storage tank layout of liquefied hydrocarbons should be designed in accordance with the applicable scope of GB50160, the design fire protection code for petrochemical enterprises. In principle, it should not be designed according to construction regulations.
Reply #82009-03-13
Forgot to mention, I am using a horizontal storage tank, and there is nothing written on that article...
Reply #92009-03-13
I agree with LS, liquefied hydrocarbons should refer to the "Petrochemical Regulations". In the "Construction Regulations", liquefied hydrocarbons are not classified. Instead, liquids with a flash point less than 28 degrees are classified into Category A. However, it is obvious that liquefied hydrocarbons are more dangerous (the "Petrochemical Regulations" classify them into Category A). Therefore, the pump should be placed outside the fire embankment in strict accordance with the "Petrochemical Regulations". In addition, I personally feel that the tank farm refers to an area, not just the fire embankment.
Reply #102009-03-13
Is there a classification in the "Building Regulations"? Is it liquefied petroleum gas? Please tell me. This post was last edited by sssshack on 2009-3-13 14:24 ]

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.